High ZE compared to SSE figures on a TN-S

Hi, I'm carrying out a periodic EICR on a factory, can any inform me of the correct procedure for gaining a ze at  origin as I have always used the 2 wire method with main earth removed as stated in the on site guide, I have a reading of 0.77 ohms on a TN-S which is no where near the 0.22 ohms that SSE has recently recorded as they had to attend to the newly installed service head ( 5 years old ) due to some loose connections. The only way that I can get my readings that low is to use the 3 wire method.

Parents
  • called out SSE who found loose connections in their equipment, they then obtained a ze of 0.22 ohms. I went back to site on Mon expecting a lower ze than what we originally recorded but it was more or less the same,

    Maybe the gremlins have come back and loosened it again? (or less charitably, it wasn't re-tightened properly, or the thread has been stripped so any attempted re-tightening produces only a temporary improvement at best, or there are several joints that weren't tightened up properly in the first place)

       - Andy.

Reply
  • called out SSE who found loose connections in their equipment, they then obtained a ze of 0.22 ohms. I went back to site on Mon expecting a lower ze than what we originally recorded but it was more or less the same,

    Maybe the gremlins have come back and loosened it again? (or less charitably, it wasn't re-tightened properly, or the thread has been stripped so any attempted re-tightening produces only a temporary improvement at best, or there are several joints that weren't tightened up properly in the first place)

       - Andy.