minimum CSA for a 1.5mm CPC in 2.5/1.5 twin & earth cable.

Doing an EICR today and two ring finals dead tests indicated that the CPC was exactly half the CSA of the line and neutral. If it had been old cable I wouldn't be surprised. But one was wired with brown/blue and the other relatively new looking red/black, They should have been 2.5/1.5. When I measured the cable with a micrometer the cpc worked out at a csa of about 1.2mm and the main conductors 2.5mm.

Not an issue from a safety point of view as it was on a TT earth with low fault currents, but then I started to think what is the allowed minimum and maximum diameter/csa of the cores according to british standards and I haven't been able to find any data, hope others can point me in the right direction.

Parents
  • When I measured the cable with a micrometer the cpc worked out at a csa of about 1.2mm and the main conductors 2.5mm

    Not answering your query, but within the last 5 years or so, I suspect many cables are not made to the relevant standards. This was clear to me a few years ago when crimping 16mm cable. Previously the crimps were quite a tight fit on the cable when put on to be crimped, but i had one reel that was very loose, in so far as I thought it was 10mm. The 10mm crimp wouldnt go on, so it was larger that 10mm, but I suspect it was more like 12 or 13mm CSA rather than 16mm.

    The cable originated from Turkey, suppled by CEF. We're currently using 2.5 and 4 mm singles supplied by CEF, made in India, and I have to read the writing on the cable to determine the CSA, as the difference is so small, whereas in the past, I could easily tell the difference between the two by looking at the conductors.

Reply
  • When I measured the cable with a micrometer the cpc worked out at a csa of about 1.2mm and the main conductors 2.5mm

    Not answering your query, but within the last 5 years or so, I suspect many cables are not made to the relevant standards. This was clear to me a few years ago when crimping 16mm cable. Previously the crimps were quite a tight fit on the cable when put on to be crimped, but i had one reel that was very loose, in so far as I thought it was 10mm. The 10mm crimp wouldnt go on, so it was larger that 10mm, but I suspect it was more like 12 or 13mm CSA rather than 16mm.

    The cable originated from Turkey, suppled by CEF. We're currently using 2.5 and 4 mm singles supplied by CEF, made in India, and I have to read the writing on the cable to determine the CSA, as the difference is so small, whereas in the past, I could easily tell the difference between the two by looking at the conductors.