Just seeking a wee bit of clarification on I delta m. Literature indicates that it is the maximum breaking capacity of residual current as distinct from the maximum breaking current. Just not sure how to interpret that.
Just seeking a wee bit of clarification on I delta m. Literature indicates that it is the maximum breaking capacity of residual current as distinct from the maximum breaking current. Just not sure how to interpret that.
This is a RCD so breaks only one kind of fault. Are they suggesting 1000A if no death and glory 100A fuse but 10000A with one? I have searched a lot of literature but cannot find a definitive answer.
I think that is probably what it means.
This link may help - see page 11.
As I understand it, Im is the rated breaking capacity and IΔm is the rated residual breaking capacity.
Confusingly, in BS7671, Im is something completely different.
I think that is probably what it means.
This link may help - see page 11.
As I understand it, Im is the rated breaking capacity and IΔm is the rated residual breaking capacity.
Confusingly, in BS7671, Im is something completely different.