Power cable connection on a mobile installation to External equipment using a MIL-DTL-38999 connector.

So I've inherited a a mobile installation project. The power cable connection on to External control equipment uses a dedicated port with a MIL-DTL-38999 connector. 

The inrush when the charging system is engaged trips the RCD when it is set to 30mA. My predecessor determined that the connection is not classified as a socket and increased the RCD trip current to 300mA.

Given that it uses the 38999 connectors and it is solely dedicated to the dismounted control systems that form part of the system is this a valid assessment? 

Parents
  • The regulations  say "Socket-outlet. A device, provided with female contacts, which is intended to be installed with the fixed wiring, and intended to receive a plug. A luminaire track system is not regarded as a socket-outlet system.", is it part of the fixed wiring?

Reply
  • The regulations  say "Socket-outlet. A device, provided with female contacts, which is intended to be installed with the fixed wiring, and intended to receive a plug. A luminaire track system is not regarded as a socket-outlet system.", is it part of the fixed wiring?

Children
  • Strictly it may also not really be part of the fixed installation either - in some sense it may be classified as a product, or as a piece of machinery.. But an ambiguous legal position does not justify not evaluating the risk technically. 

    Note that some of the 38999 socket patterns are have contacts you can touch with a finger  exposed at the mating face - while others are deeply recessed and meet clearance requirements.

    Here is a catalogue page showing just  a few and a photo that illustrates the point.

    Mike

  • Sorry to be so vague, there is only so much I can say. The installation is mobile, and yes I agree re the risk assessment hence a full risk assessment was done. My problem is that regulation 411.3.3 clause (iii) state that mobile equipment not exceeding a current rating of 32A for use outdoors has to use a current rating not exceeding 30mA for socket outlets and the risk assessment exception clause does not apply to it. Hence the question as to if we can class it a part of the installation.

    The connector is a series 3 connector and is designed so that the pins cannot be touched accidentally and for extreme weather conditions.

     It connects on the front of one of the installations  power system units to provide power to the control systems that have to be dismounted a given distance away for safety reasons. So when you look at the system as a whole it is one system. Frustratingly I think we fall into a grey area when it comes to classifying it as a socket or part of the installation.

  • If you mean BS7671, then sockets that are part of the fixed wiring installation that supply mobile equipment have to be RCD protected.  But I am presuming this whole rig does not connect to the mains that way ? Can you say if it has a built in generator - and so is powered while mobile, and not just when parked up.

    Those 'wiring' regs do not generally apply to any sockets that are part of the equipment itself - that would probably fall under the machinery directive instead, unless we are looking at 13A sockets in a caravan or a Portakabin type thing , when it is sort of a fixed installation for use by ordinary folk again. 

    A 30mA instant RCD may not work but if it is really just an inrush issue, then a delay type of programmable earth fault relay example  operating a contactor in the supply might, and still afford adequate and regs compliant protection, as you can meet the 30mA requirement safety of life thing with up to a 0.2 second delay ( or 0.4 secs in some cases)


    Mike.

  • yes it has an onboard generator, no it is not powered up while on the move, just when stationary.

    We discovered recently that the designer of the generator unit used a 1/500 winding current transformer when they should have used a 1/1000. This means it was actually tripping at just under 15mA  - no surprise it couldn't take the inrush. (Long and tedious story. Please don't suggest the supplier changes it, been there done that still have a bleeding forehead from repeatedly banging my head against the wall.)

    None of the RCD setting adjustment process from the Dev stage was written down (before my time), so I don't know if they gradually turned it up or just went straight to 300mA. Whether they tried a time delay I really couldn't say. The RCD does have detents at 100mA etc, and an adjustable time delay. We are going to have to go through that process now to determine if a lower setting would work. The lower the better in my opinion. 

    I think in the mean time I'm going to have to go with 'It's not a general use socket and is a specialised connector supply one aspect of the system only' for now. Therefore not a socket in the sense that the regs mean.

  • I'd also play the for use by  'skilled and instructed persons only' card as well if you can. It is really not after all anything like a socket for use by ordinary/unskilled persons.
    Indeed it is not being plugged and unplugged at all while genset is on I imagine? 

    Fully understand the difficulty of changing the plans after something has been built and delivered - concession forms and engineering change costs etc. 

    Mike.

  • The regulations  say "Socket-outlet. A device, provided with female contacts, which is intended to be installed with the fixed wiring, and intended to receive a plug. A luminaire track system is not regarded as a socket-outlet system.", is it part of the fixed wiring?

    BS 7671 also defines a cable coupler. This pairing has a 'plug' and a 'connector' ... however, this connector doesn't have an IEC, CENELEC or British standard ... so, to use them in an electrical installation for which BS 7671 applies (including those to BS 7909) would require a declaration of some sort (see BS 7671, Regulation 133.1.1 and Section 511).

    Given that it uses the 38999 connectors and it is solely dedicated to the dismounted control systems that form part of the system is this a valid assessment? 

    Are the 'control systems' part of an electrical installation, or Machinery as defined in the Supply of Machinery (Safety) Regulations? If the latter, then BS EN 60204-1 might apply, rather than BS 7671?

  • The regulations  say "Socket-outlet. A device, provided with female contacts, which is intended to be installed with the fixed wiring, and intended to receive a plug. A luminaire track system is not regarded as a socket-outlet system.", is it part of the fixed wiring?

    BS 7671 also defines a cable coupler. This pairing has a 'plug' and a 'connector' ... however, this connector doesn't have an IEC, CENELEC or British standard ... so, to use them in an electrical installation for which BS 7671 applies (including those to BS 7909) would require a declaration of some sort (see BS 7671, Regulation 133.1.1 and Section 511).

    Given that it uses the 38999 connectors and it is solely dedicated to the dismounted control systems that form part of the system is this a valid assessment? 

    Are the 'control systems' part of an electrical installation, or Machinery as defined in the Supply of Machinery (Safety) Regulations? If the latter, then BS EN 60204-1 might apply, rather than BS 7671?

    Semantics again!

    Is it an electrical installation or a machine? Or neither?? My first thought was whether this equipment is in scope or not. 110.1.1 says that the Regulations apply to electrical installations, so if it is not one, BS 7671 does not apply.

    Is the device in question a "socket-outlet". Newfutile questioned this. I think that it is difficult to get away from the connexion being a socket and plug, but I am far from convinced that it is a "socket-outlet" as defined. More importantly, 411.3.3 is all about supplying electrical energy (the Grid in a building, PV, generator, WHY) from a socket upstream to an appliance downstream.

    Most things are mobile if you have the capacity. I envisage a "machine", for want of a better word, which can be transported (perhaps to a battlefield, or more importantly, an exercise area), but which has to be broken down into components to make it mobile. If you didn't use some form of plug and socket, how else would you put it together? (I discount the notion of terminal blocks in enclosures.)

  • Be aware that there are significant relaxations of the machinery directive, & it is completely dis-applied for fairground, police or military equipment, or several kinds of vehicle, though generally not otherwise normal equipment that just happens to be mounted on a vehicle.

    quoting the 2023 version.

    2.  This Regulation does not apply to:
    (a)   safety components that are intended to be used as spare parts to replace identical components and are supplied by the manufacturer of the original machinery, related product or partly completed machinery;
    (b) specific equipment for use in fairgrounds or amusement parks;
    (c) machinery and related products specially designed for use within or used in a nuclear installation and whose conformity with this Regulation may undermine the nuclear safety of that installation;
    (d) weapons, including firearms;
    (e) means of transport by air, on water and on rail networks except for machinery mounted on those means of transport;
    (f) aeronautical products, parts and equipment that fall within the scope of Regulation (EU) 2018/1139 of the European Parliament and of the Council ( 1 ) and the definition of machinery under this Regulation, insofar as Regulation (EU) 2018/1139 covers the relevant essential health and safety requirements set out in this Regulation;
    (g) motor vehicles and their trailers, as well as systems, components, separate technical units, parts and equipment designed and constructed for such vehicles, which fall within the scope of Regulation (EU) 2018/858, except for machinery mounted on those vehicles;
    (h) two- or three-wheel vehicles and quadricycles, as well as systems, components, separate technical units, parts and equipment designed and constructed for such vehicles, that fall within the scope of Regulation (EU) No 168/2013, except for machinery mounted on those vehicles;
    (i)  agricultural and forestry tractors, as well as systems, components, separate technical units, parts and equipment designed and  constructed for such tractors, that fall within the scope of Regulation (EU) No 167/2013, except for machinery mounted on those tractors;

    (k) seagoing vessels and mobile offshore units and machinery installed on board such vessels or units;

    (l) machinery or related products specially designed and constructed for military or police purposes;
    (m) machinery or related products specially designed and constructed for research purposes for temporary use in laboratories;
    (n) mine winding gear;
    (o) machinery or related products intended to move performers during artistic performances;
    (p) the following electrical and electronic products, insofar as they fall within the scope of Directive 2014/35/EU or of Directive 2014/53/EU:
      (i) household appliances intended for domestic use which are not electrically operated furniture;
      (ii) audio and video equipment;
      (iii) information technology equipment;
      (iv) ordinary office machinery, except additive printing machinery for producing three-dimensional products;
      (v) low-voltage switchgear and control gear;
      (vi) electric motors;
    (q) the following high-voltage electrical products:
      (i) switchgear and control gear;
      (ii) transformers.
    not sure if that helps
    Regards Mike.