BS-5839 part 6 LD3

Does BS-5839 part 6 LD3 need to be reviewed?  Points to consider.

LD3 is considered the Minimum Protection for a domestic dwelling.

Normally in a 3 bed semi detached house Detectors are in all circulation areas that form part of the escape routes (hallways and landings) ONLY.  Would/Could it beneficial to include or mandate a heat alarm for the kitchen and/or plant room if present?  (Plant room could contain kit from Solar PV battery storage or inverter etc)

LD3 also seems to infer that the fire will/could start inside the dwelling rather than elsewhere.  As an couterargument example an e-bike may be left directly outside the front door or rear door.  Does LD3 take into full consideration the shear amount of electrical and electronic items now in the average dwelling?  Most dwellings will contain at least 1 mobile phone which may or may not be left charging overnight, same could be said for a laptop or tablet or small battery pack (20000mAh USB Power Bank or less).  With direct reference to the small battery pack reference is made to the fact that China requires CCC certification for power banks sold within the country and strictly prohibits non-CCC certified, unclear, or recalled power banks on domestic flights.


LD3 seems to only really apply in England & Wales as Scotland changed their law in 2022.  In Scotland every home (owner-occupied, private rented, social housing, and new build) must meet a minimum standard that is functionally equivalent to Category LD2.



As always please be polite and respectful in this purely academic debate.





Come on everybody let’s help inspire the future.

Parents
  • Dwelling fires are still falling in England from 28,504 in 2019/2020 to 25,408 in 2024/2025. That said the number of fatalities is creeping up 194 in 2024/2025 compared to 166 in 2023/2024 and 199 in 2022/2023

    (source assets.publishing.service.gov.uk/.../FIRE0205.xlsx)

    The guidance that supports the building regulations ADB v1 still up to 2029 only requires LD3.

    BS 5839-6 does recommend a risk assessment before picking a category. And categories are short hand not straight jackets adding a extra detector does mean its becomes another category.

    BS 5839-1:2019 + A1:2020 recommends LD2 for new dwellings. Plus it is starting its review in January so start your ideas on how it should be changed now!

  • the approved documents are not law only guidance

    Quite so, but your quotations from Schedule 1 of the Building Regulations 2010 are law. Contravention may lead of a fine of up to £5k, or two years' imprisonment, or both - see S.35 of the Building Act 1984.

  • This is for ENGLAND ONLY other nations have diferent rules

    The laws and guidance/regulations need to take into account the following variants as an example

     - Average 3 bed Semi lived in by an average family built lets say 100 years ago

    legally no detection needed. current guidance battery only smoke/heat alarms interlinked LD3 unless you are rewiring then mains powered with battery back up smoke/heat alarms to LD2

     - Average 3 bed Semi lived in by an average family which INCLUDES a member with lesser abilities be that physical/mental built lets say 100 years ago.  (My wording may not be politically correct but listen to the intent rather that focus on the words I have used)

    as above but with the extra need in guidnace to do a risk assessment for which there is annex on what should be considered 

    - Average 3 bed Semi lived in by an average family on a RENTAL Basis built lets say 100 years ago

    legally one smoke detector on each level do not have to be interlinked. Current guidance mains powered tamper proof battery smoke/heat detctors interlinked LD2

    - Average 3 bed Semi lived in by an average family on a RENTAL Basis which INCLUDES a member with lesser abilities be that physical/mental built lets say 100 years ago.  (My wording may not be politically correct but listen to the intent rather that focus on the words I have used)

    as above but with the extra need in guidnace to do a risk assessment for which there is annex on what should be considered 

    if you think this all a bit of a mess? welcome to my world and we haven't even mentioned section 257 HMO's under the Housing Act 2004

  • "in a word money."

    Quite, and if labour was free and materials were free, we'd all live in mansions with hot and cold running servants.  Oddly we don't.
    And the question then becomes more nuanced - 'what is this measure worth?' and of course ' could we do more good overall if we spent the same money elsewhere?' And this is a painful balance for some because although folks will say one death is too many (and perhaps if it is them or their loved one whose life was lost, it is) you cannot design a policy based on that. If we did, then maybe  we'd still have a man with a red flag walking in front of every car and electricity and gas would be banned.

    What changes over time is what level of protection is cost -effective, and rather like what sort of medicines the NHS will pay for, that depends partly on the value placed on a life and partly on how the materials cost tend to fall over time.
    So If you think one life saved is say 1 million pounds (and that is probably not true but hey ho), but installing a basic fire detection system costs say £50 (battery smoke alarms on double sided tape) then only one in every 20,000 such systems needs to save a life for the exercise to have been worthwhile. But a more complex  system costing say £500 to install is not worthwhile unless you can be sure that for every 2000 systems you install, a life is saved. 
    As noted cost to retrofit is far higher than to fit to new build, but even new build the cost is still not zero.
    But things like wireless linked bases may lower the cost of something more sophisticated that was once too expensive, back to being worthwhile again.

    So what has changed in terms of cost per given efficacy, and have we raised the value of life ?
    I'm not trying to be callous, but this is the way to prove you are not squandering money on fire alarms that may have been better spent on (say) water temperature alarms or anti mould measures or some other non-electrical matter.
    The usual problem is we don't usually have enough data to be sure until after the decision has been implemented.
    Mike.

  • What changes over time is what level of protection is cost -effective, and rather like what sort of medicines the NHS will pay for, that depends partly on the value placed on a life and partly on how the materials cost tend to fall over time.
    So If you think one life saved is say 1 million pounds (and that is probably not true but hey ho), but installing a basic fire detection system costs say £50 (battery smoke alarms on double sided tape) then only one in every 20,000 such systems needs to save a life for the exercise to have been worthwhile. But a more complex  system costing say £500 to install is not worthwhile unless you can be sure that for every 2000 systems you install, a life is saved. 
    As noted cost to retrofit is far higher than to fit to new build, but even new build the cost is still not zero.
    But things like wireless linked bases may lower the cost of something more sophisticated that was once too expensive, back to being worthwhile again.

    Not sure I fully agree there Mike.  When I was growing up in the UK in the 1970 and 80s few house domestic houses had smoke alarms.  Any that did probably only had 1 for the whole house.  Now in the 1980 I remember campaigns to get a smoke alarm for your home for your family safety.   BUT the push became significantly stronger in the 1990s following new UK building regulations.  

    These days people understand from past history/campaigns/building regulations and general awareness that 2 smoke alarms in the average 3 bed semi is more prudent.  I do agree that the cost of smoke alarms has reduced.  

    As an example

    Screwfix do a battery operated smoke alarm £6.99 as it most basic offering (Smith & Locke KD-129H Battery Standalone Smoke Alarm (747CG))

    or 

    Hispec Fast Fix PE/FF Mains Interlinked Optical Smoke Alarm (361RG)  £18.50

    Other brands and other wholesalers are availabel

    Thus for less than £100 you could get 3 interlinked mains units with battery backup for an average domestic dwelling.  IF mains power is cost prohibative due to labour or build fabric them battery power and interlinked is still an option but fractionally more exspensive but lets say less the £150.  So I put it to you and the community at large.  

    What is the cost/value of the/a person for an average 3 bed semi against £150.  Remember, people are not just values or numbers, they are someones family or loved ones.

  • What changes over time is what level of protection is cost -effective, and rather like what sort of medicines the NHS will pay for, that depends partly on the value placed on a life and partly on how the materials cost tend to fall over time.
    So If you think one life saved is say 1 million pounds (and that is probably not true but hey ho), but installing a basic fire detection system costs say £50 (battery smoke alarms on double sided tape) then only one in every 20,000 such systems needs to save a life for the exercise to have been worthwhile. But a more complex  system costing say £500 to install is not worthwhile unless you can be sure that for every 2000 systems you install, a life is saved.

    I have a figure of £1m at the back of my mind, but we could say £2m to account for inflation.

    These alarms do not prevent fires, nor do they put them out. We could add injuries to people and property to the equation, but it seems that the BS 5839 systems are intended to allow occupants (more) time to escape. So, if the aim is to reduce mortality, it begins to look like a public health question and it is indeed, "rather like what sort of medicines the NHS will pay for".

    It seems beyond doubt that reducing excessive blood pressure (hypertension) reduces the risk of stroke and heart attack. If a pharmaceutical company wanted to bring a new anti-hypertensive to the market, it would have to show that it was more effective (in terms of mortality or morbidity) or at least as effective, but cheaper than existing drugs. So they are not comparing new drug against nothing, but new against old. Undoubtedly, a randomised controlled trial would be involved from which number needed to treat could be calculated.

    Similarly, one could compare LD2 and LD3 protection: how many LD2 systems need to be installed to save one extra life?

    But now we have a problem. Could we do a randomised controlled trial? One of the Government's proposed new towns would do. Fit half the properties to LD2 and half to LD3. Then, ignoring any ethical considerations, wait 50 years and hope that sufficient fires break out to allow a meaningful comparison.

  • What is the cost/value of the/a person for an average 3 bed semi against £150.  Remember, people are not just values or numbers, they are someones family or loved ones.

    So for say, 20 million houses in the UK (there may be more by now) that's £ 3 BILLION - what could be done with that sort of money? Cure for another cancer? Thousands of urgent operations brought forward? Better care for the elderly? Are you going to tell their loved ones that they're less worthy than a plastic box on loads of people's ceiling's that 99.99% of the time provides no benefit whatsoever?

    No easy answers.

      - Andy.

  • The link did not work for me, but I think that I have found the data.

    I was going to ask how many of you have experienced a building fire, but ...

    25,000 fires per year does not seem a huge number. However, given that there are 50-odd million of us, and allowing for an average household of two, that is a chance of being in a dwelling on fire in any year of approximately 1:1000, or 1:20 over 50 years.

    I have had my experience! In fact the fire was in the landlord's quarters in my local (as in next door) pub about 45 years ago. If there was an alarm system, it was not installed there. When the alarm was raised - smoke was pouring out of the bedroom window - I dashed upstairs with a fire extinguisher, but the fire was way beyond that.

    Happily, nobody was injured and rather unexpectedly, the pub was open for evening service.

    No alarm would have made any difference, but the 2nd floor was used for B&B accommodation, and IIRC, any escape route would have been past the bedroom door.

    I think that in this instance, LD2 would not have helped, but LD1 could have made a difference.

    Back to Will's data: a drop of a third in the number of fires over 15 years seems impressive. However, as with the reduction in mortality due to stroke and heart attack, it may have more to do with the reduction in smoking rather than any other intervention.

  • I am not sure why it would cost the government or the people £ 3 BILLION.  As I stated previously you could get the kit from ScrewFix (other sellers are also available) for an interlinked system for between £100 to £200 for the average 3 bed semi 

  •  Afraid that Andy's figure seems to assume that nobody has any smoke detectors/alarms yet!

    HMG promises to build (i.e. hoping that the private sector will build) 1.5 million homes during its 5 years in office. So at £150 a pop, that is £225 million.

    One really good jackpot in the Lottery!!!

  • So the parts alone are £200, what does it cost to retrofit to a building and then make good ? I presume perhaps a day, maybe two, so more like 300-400 all up.  So we do that for 20 million house-holds and that is 20*300 = 6000 million, maybe 20*400 - 8000  so between  6-8 billion. You are right - it would be a serious investment.

    Could we save enough extra  lives over the life of such an investment  (perhaps 10-20 years) compared to that money spent another way?  After all the folk dying from all the other things we don't do instead so we can afford to do just this are also someone else's loved ones. There is no truly free lunch. 

    I'm not saying we should not uplift the recommended standards - far from it,  just that there is an argument for putting our money most carefully where it has most effect  - cost benefit analyses are not some obscure excuse not to do things, they do serve a very real purpose. We do need to be able to clearly justify why a more complex and expensive recommendation is to be preferred.

    To my mind Chris's thought experiment is correct, but very hard to sell morally.

    Mike. 

Reply
  • So the parts alone are £200, what does it cost to retrofit to a building and then make good ? I presume perhaps a day, maybe two, so more like 300-400 all up.  So we do that for 20 million house-holds and that is 20*300 = 6000 million, maybe 20*400 - 8000  so between  6-8 billion. You are right - it would be a serious investment.

    Could we save enough extra  lives over the life of such an investment  (perhaps 10-20 years) compared to that money spent another way?  After all the folk dying from all the other things we don't do instead so we can afford to do just this are also someone else's loved ones. There is no truly free lunch. 

    I'm not saying we should not uplift the recommended standards - far from it,  just that there is an argument for putting our money most carefully where it has most effect  - cost benefit analyses are not some obscure excuse not to do things, they do serve a very real purpose. We do need to be able to clearly justify why a more complex and expensive recommendation is to be preferred.

    To my mind Chris's thought experiment is correct, but very hard to sell morally.

    Mike. 

Children
  • In the simplest form you could have a battery power smoke alarm with RF interlink upstairs on the landing, the same downstairs near the front door and a heat alarm/sensor in the kitchen.  By choosing battery powered with RF interlink it means that each unit only really needs to 2 to 4 screws and the same amount of Raw plugs (other brands of fixing are also available).  Then upto 2 hours of labour to install and commission.

    The caveat that most people forget is that the domestic smoke alarm / heat alarm / multi sensor alarm is only valid for 10 years max.  After this the sensor is deemed no longer accurate by the manufacturer.

    Overall the cost is not that much for the average household/family living in the average 3 bed semi that they own/mortgage.

  • In the simplest form you could have a battery power smoke alarm

    Not if you want to comply with the Building regulations: they require mains-powered alarms.

    The caveat that most people forget is that the domestic smoke alarm / heat alarm / multi sensor alarm is only valid for 10 years max.  After this the sensor is deemed no longer accurate by the manufacturer.

    Or the battery is no longer reliable.

  • Not if you want to comply with the Building regulations: they require mains-powered alarms.

    This is another reason this discussion was started.  See first line of my post.  Does BS-5839 part 6 LD3 need to be reviewed? 

    Current/updated Building Regulation and BS-5839 part 6 need to match as BS7671 refers out to BS-5839 part 6 and the whole BS-5839 series throughout

  • At the moment the advice is inconsistent - and of course building regs are normally only considered when there is actual building or renovation work going on for another purpose that requires inspection. Personally I think that then, like new build, the threshold of how much is reasonable to do and disrupt is quite a bit higher than an upgrade to an existing property with folk living in with their carpets and  furniture in place and so on.

    And I'd agree I think with the current costs of stuff and labour, a stand alone or  interlinked by wireless battery set is probably just about OK for the latter, and drilling holes and pulling wires is more suited to renovations and new builds and similar "major" works.

    Mike

  • This is another reason this discussion was started.

    Yes, but the Grade (A to F) is independent of the Category (LD1 to LD3).