Checking Iz
From BS7671
Method is used in items 5.1 and 5.2 Ib or In / Correction factors
But it is possible to get incorrect coordination with cable calculations that seem acceptable?
Thanks so much.
I do get (i think) When selecting a cable, dividing the (In or Ib) by the correction factors gives us the minimum tabulated rating required, so harsher installation conditions will push (It) upwards.When verifying a chosen cable, multiplying the tabulated rating by the correction factors gives the actual derated capacity, so the same harsh conditions drive Iz downwards.
They should roughtly do the same job, but the It≥ C is a quicker method
Thanks so much.
I do get (i think) When selecting a cable, dividing the (In or Ib) by the correction factors gives us the minimum tabulated rating required, so harsher installation conditions will push (It) upwards.When verifying a chosen cable, multiplying the tabulated rating by the correction factors gives the actual derated capacity, so the same harsh conditions drive Iz downwards.
They should roughtly do the same job, but the It≥ C is a quicker method