Checking Iz
From BS7671
Method is used in items 5.1 and 5.2 Ib or In / Correction factors
But it is possible to get incorrect coordination with cable calculations that seem acceptable?
You need to decide if overload protection is needed or not - if so you start with In rather than Ib.
Thank you.
I think there are two different ideas getting mixed up here and making things look more complicated than they need be.
Firstly there's the idea of choosing "how much current you need the cable to carry" - if it only needs to carry what the load normally draws, then you can use Ib, if on the other hand it may need to carry more than that, up to the limit of the protective device (i.e. overload protection is needed) then you use the rating of the protective device - In.
Quite separately from that, there's the relationship between the cable's current carrying capacity in "standard" conditions (i.e. as tabulated, before applying correction factors) and that it will actually have under the conditions it's installed in (Iz).
The "obvious" way to calculate things might be to take the tabulated value, multiply by all the correction factors and compare that with "how much current you need the cable to carry". The trouble with that approach (especially in the days when electrician's didn't have a computer to hand) is that you end up having to do the same calculation umpteen times over to check a variety of cable sizes.
So they came up with an alternative approach of doing the calculation the "other way around" - i.e instead of calculating how much each size of cable could carry under the actual conditions, you'd instead calculate what the current carrying capacity of a just-the-right size cable would be if it was installed under standard conditions instead of the actual conditions - because you can then calculate one value and look it up in the tables once.
That might sound a bit odd, but mathematically it's quite simple - instead of multiplying two numbers to give a final answer, you take the final answer and divide by one number to give you the other.
So instead of calculating Iz for each cable size as It * C (and compare the result with "how much current you need the cable to carry"),you'd take "how much current you need the cable to carry" and divide by the correction factors to give you what would be the "tabulated" value of your ideal cable - you just then look up a size that's no smaller than that.
does that make things any clearer?
Thanks so much.
I do get (i think) When selecting a cable, dividing the (In or Ib) by the correction factors gives us the minimum tabulated rating required, so harsher installation conditions will push (It) upwards.When verifying a chosen cable, multiplying the tabulated rating by the correction factors gives the actual derated capacity, so the same harsh conditions drive Iz downwards.
They should roughtly do the same job, but the It≥ C is a quicker method
But I keep seeing Ib ≥ In ≥ Iz as the ‘big thing’
Hopefully the other way around: Ib ≤ In ≤ Iz (a small, but very significant difference!), but yes (where overload protection is required) that's the fundamental requirement. That doesn't mean you have to go about calculating it in that direct manner though - as long as the result you come out with satisfies that requirement, all is well. It's rather like saying you need to show that 1 ≤ 2 ≤ 3, but you've only got the figures 10, 20 and 30 instead - you could divide everything through by 10 and prove it, but you can also see directly that the same relationship will hold true. In our case things are multiplied (or divided) by all the correction factors, rather than 10, but the same logic holds. If it's true that "how much current you need the cable to carry" ≤ Iz then it must also be true that ("how much current you need the cable to carry" divided by C) ≤ (Iz divided by C) (for any positive value of C).
But it appears to me that (Iz) is not really established
Indeed - with the 'alternative method' you only establish your minimum acceptable figure for Iz (which is the same as "how much current you need the cable to carry") you don't need to calculate Iz of the actual cable size you select. Because the cable size you actually select can't be smaller than the theoretical "just the right size" cable calculated, the actual Iz of the chosen cable can't possibly be smaller than your minimum acceptable figure, so you can be sure the requirement is met even without calculating the exact figure.
Sorry, this must be painful for you.
It is worth noting that not all books use the same notation for the letters, although these days mostly they do, and I find it helpful to have a 'plain language' description of what is happening.
or the protective device might trip during normal operation, and
which is the cable's rating.
Or the cable may be overloaded.
Of course once exams are passed you then will realise its not really always true - the limiting of the load current could just as well be at the load end or the origin - Perhaps consider a single 13A fused spur, on 2.5mm2 fed by a 20A or even 32A MCB will be fine, as the 13A fuse means the cable cannot be overloaded even though the circuit protection appears to be 32A.
More generally odd socket circuits are usually the ones where it is hard to be sure as you are often not really sure what might one day be plugged in and it maybe looks a if the breaker is too small, - perhaps a single 20A breaker feeding half a dozen BS4343 style 16A sockets for kit in a small workshop looks undersized, when the nature of the loads and the use pattern means it really isn't.
Then there is the matter that short duration overloads like motor startup in-rush may trip the breaker, but assuming they don't, the cable is fine with it, as it takes several minutes to warm a large bundle of cables and the grouping derating can be pushed quite a lot, if cables are not all fully loaded at once for a long time.
It is certainly worth keeping your wits about you above and beyond the algebra.
Not at all!
But I think I’ve got it.
It is basic transposition.