Do we not get into a merry-go round of confusing desired (designed in) 'leakage' such as that from EMC filters (tripping undesired), and the undesired 'leakage' fault currents, particularly accidental touch based leakages for which tripping is clearly desired?
It wasn't clear to me what the 30% figure alluded to. Is it the lowest level of leakage (either style) that might trip the RCD? Could it be the maximum level of designed-in leakage from all the filters?
The steady inclusion of more an more EMC (HF) filters can greatly increase the level of 'leakage' with the potential for nuisance trips. And that's before any of the Heat pump EMC filter problems (the ~1kHz band).
The modern house is definitely a complex system that needs some thought.
I think the 30% comes from 531.3.2 - so avoiding "Unwanted tripping" - as RCDs can trip anywhere between 50% and 100% of their residual rating, I suppose it gives a bit of a margin.
I'd be wary of blanket bans on "shared RCDs" - there are situations - i.e. RCD protection on a sub-main in TT systems, where one RCD "shared" across several final circuits in pretty much unavoidable - and can be OK if done carefully.
By the looks of it BS 7671 already provides enough evidence that multiple high leakage appliances on a single 30mA RCD isn't compliant.
- Andy.
I think the 30% comes from 531.3.2 - so avoiding "Unwanted tripping" - as RCDs can trip anywhere between 50% and 100% of their residual rating, I suppose it gives a bit of a margin.
I'd be wary of blanket bans on "shared RCDs" - there are situations - i.e. RCD protection on a sub-main in TT systems, where one RCD "shared" across several final circuits in pretty much unavoidable - and can be OK if done carefully.
By the looks of it BS 7671 already provides enough evidence that multiple high leakage appliances on a single 30mA RCD isn't compliant.
- Andy.
Hmm, 10mA of idle state leakage on a 30mA RCD spanning many final circuits is not great design even so. Elsewhere (not the UK) I have seen RCDs for general loads chosen based on 0.1% - so 1mA per amp - 30mA RCD on a 30A circuit etc.
Does not really work so well here as a rule of thumb with with ring finals and single phase 100A boards.
Mike.
I think that Andy has summed up the engineering succinctly.
If the leakage currents in the dual-RCD boards are excessive, then there would be a lot of nuisance tripping. Is that actually the case?
What is the economic argument? I doubt that margins are so fine on new-build developments that all-RCBO boards cannot be provided. With after-market solar PV installations costing £thousands, once again a few £tens more on a board change hardly matters.
Of course, should nuisance-tripping materialize, the householder would have to stump up the cash to rectify the problem. That may seem like money well-spent, but would hardly be fair on a tenant.