My war against dual rcd boards

As each (RCD) Residual Current Device must not have more than 30% leakage current on it.
It's hard to see how dual (RCD) Residual Current Device boards can be fitted at all these days.
i come across so many dual rcd boards with solar, evse and heat pumps on them, these have all been recently installed.
i wonder if BS7671 should state: Dual (RCD) Residual Current Device boards shall not be fitted, unless it can be shown (and documented) that they are suitable for the combined leakage currents expected .
otherwise developers will keep specifying them and i will have keep educating them on the many reasons a type A rcd should not be shared with other equipment!.
maybe manuafactuers instructions should also state : not suitable for a shared rcd, for certain equipment.
Parents
  • Do we not get into a merry-go round of confusing desired (designed in) 'leakage' such as that from EMC filters (tripping undesired), and the undesired 'leakage' fault currents, particularly accidental touch based leakages for which tripping is clearly desired?

    It wasn't clear to me what the 30% figure alluded to. Is it the lowest level of leakage (either style) that might trip the RCD? Could it be the maximum level of designed-in leakage from all the filters?

    The steady inclusion of more an more EMC (HF) filters can greatly increase the level of 'leakage' with the potential for nuisance trips. And that's before any of the Heat pump EMC filter problems (the ~1kHz band). 

    The modern house is definitely a complex system that needs some thought.

  • Hmm, 10mA of idle state leakage on a 30mA RCD spanning many final circuits is not great design even so. Elsewhere (not the UK)  I have seen RCDs for general loads chosen based on 0.1%  - so 1mA per amp - 30mA RCD on a 30A circuit etc.
    Does not really work so well here as a rule of thumb with with ring finals and single phase 100A boards.

    Mike.

  • I think that Andy has summed up the engineering succinctly.

    If the leakage currents in the dual-RCD boards are excessive, then there would be a lot of nuisance tripping. Is that actually the case?

    What is the economic argument? I doubt that margins are so fine on new-build developments that all-RCBO boards cannot be provided. With after-market solar PV installations costing £thousands, once again a few £tens more on a board change hardly matters.

    Of course, should nuisance-tripping materialize, the householder would have to stump up the cash to rectify the problem. That may seem like money well-spent, but would hardly be fair on a tenant.

  • Philip,

    Based on your last sentence, that must be why in the In the UK we have "Domestic Installers"! to deal with those complex systems.

    Cheers GTB

  • Is the issue due to installer or system designer.  I would say the installer does what the designer has prescribed

  • What is the economic argument? I doubt that margins are so fine on new-build developments that all-RCBO boards cannot be provided. With after-market solar PV installations costing £thousands, once again a few £tens more on a board change hardly matters

    Try and compare a Hager (other brands are available) split load CU against a Navits CU

    https://www.navitascp.co.uk/product-page/10-way-100a-mainswitch-consumer-units-c-w-t2-spd

    The economic argument goes out of the window (other Apertures are available) 

    I see no reason why a fully RCBO and SPD type2 CU can not be designed and installed in the average UK dwelling

  • Sergio,

    In my exeprience and despite what standards and regulations say, in majority of cases in domestic dwelling house work there is no "Designer". The installer or somebody may be signing paperwork as "Designer". But attitude is still very much "Its only a dwelling" what can go wrong?.

    Cheers GTB

  • Or need that little bit extra clarity, particularly about the distinctions between requirements, regulations and specifications (there's a separate thread on that  Requirement Structuring ) Smiley

  • I see no reason why a fully RCBO and SPD type2 CU can not be designed and installed in the average UK dwelling

    I entirely agree, but I would not condemn a dual-RCB on those grounds.

    In theory, any board to BS EN 61439 should be satisfactory.

    My recent shopping shows me that I can buy a turkey from Waitrose or Tesco for over £100. Currently, Aldi are offering a small turkey with accessories for £12 - link. There is no reason to believe that the Aldi turkey is less safe or less nutritious than the Waitrose or Tesco ones.

    So what is better about the Hager, or Eaton, etc. board. They might last longer, but how else could you justify the extra cost?

  • In theory, any board to BS EN 61439 should be satisfactory

    Give or take selection of it in respect of and division of installation (Section 314), and appropriate protective devices (Part 5). BS 7671 applies to the 'selection and application of the equipment in the installation concerned' (see Regulation 113.1).

  • I entirely agree, but I would not condemn a dual-RCB on those grounds.

    The point I was trying to raise was that in this day and age a new build dwelling or a major alteration of an existing domestic dwelling should have a fully RCBO with SPD type 2 CU used.  However designers are still using Split load CU for brand new installs in 2025.  As a casing point I visited a new housing developement in Hemel Hempstead last month and the show homes had split load CU’s.  The development is planned to continue building dwelling at that site for the next 2 years which I assume means that they will still be using the same split load CU at that site for the next two years.  In my opinion I would say the split load CU should no longer be marketed and sold in the UK for the average domestic dwellings.  

Reply
  • I entirely agree, but I would not condemn a dual-RCB on those grounds.

    The point I was trying to raise was that in this day and age a new build dwelling or a major alteration of an existing domestic dwelling should have a fully RCBO with SPD type 2 CU used.  However designers are still using Split load CU for brand new installs in 2025.  As a casing point I visited a new housing developement in Hemel Hempstead last month and the show homes had split load CU’s.  The development is planned to continue building dwelling at that site for the next 2 years which I assume means that they will still be using the same split load CU at that site for the next two years.  In my opinion I would say the split load CU should no longer be marketed and sold in the UK for the average domestic dwellings.  

Children
  • In my opinion I would say the split load CU should no longer be marketed and sold in the UK for the average domestic dwellings.

    I don't think that we are far apart, but as a libertarian, I would not ban them. They may have their disadvantages, but unless they are dangerous, their use should be permitted.

    So let's propose a ban: what would the counter-argument be? It seems to me that it can only be economic, and trivial at that.

    My argument in favour is libertarian - authorities (e.g. Parliament) should intervene in peoples' lives as little as possible, and people should be free to lead their lives as they see fit.

    Apart from that and the economic argument, is there any other reason to favour dual-RCD boards?