I have a 15 way dual RCD board on my home installation. I have lots of electronic equipment plus a full range of kitchen and laundary appliances, an outside workshop with machinary and a amatuer radio station. I have a standing earth leakage of 11mA acroos the 2 RCDs. Never had a nuisance trip other than the senior management pooring water over her steam iron, this got replaced with an early wedding present (she was lost for words and no dinner for me that night).
JP
And ... not all Type AC RCDs are 'blinded' in the same way, to the same thresholds.
Agreed
But we do know they (Type AC RCD) get blinded or may become blinded to a greater or less degree. Now consider the domestic dwelling for the scenario a light bulb fails (lamp to engineers) Home owner/occupier replaces it. Firstly the original lamp could of been filament or halogen or florescent/compact florescent the replacement surely by now will be LED thus the resistive load now becomes an electronic load with or without a certain amount of DC leakage.
Firstly the original lamp could of been filament or halogen or florescent/compact florescent the replacement surely by now will be LED thus the resistive load now becomes an electronic load with or without a certain amount of DC leakage.
How can you have any leakage from anything with a 2-wire connection, like a BC or ES lampholder? (and no other connection to terra firma).
- Andy.
Firstly the original lamp could of been filament or halogen or florescent/compact florescent the replacement surely by now will be LED thus the resistive load now becomes an electronic load with or without a certain amount of DC leakage
Isn't that a matter for the product standards, and relevant legislation such as the Electrical Equipment (Safety) Regulations and the Electromagnetic Compatibility Regulations? A product manufacturer ought not to assume an electrical installation conforms to the current version of the national wiring code? They can, however, provide information and guidance for users and installers that highlight certain issues, I guess - but in the case of a general product with a standard plug, or a GLS replacement lamp, would the user even understand the information?
This debate about compatibility could go on and on in other directions. We do know that older RCDs (BS 4293 and BS 7288 prior to 2016) weren't necessarily tested for Electromagnetic Compatibility to the current levels - this could also be the case for RCDs to earlier versions of BS EN 61008 and BS EN 61009 than the current versions (although I haven't checked as of posting this) ... so are they safe for continued use if modern electronic devices are used in the premises?
How can you have any leakage from anything with a 2-wire connection, like a BC or ES lampholder? (and no other connection to terra firma).
Capacitive is possible in the cabling to the ceiling rose ... but that would rule out DC, and would be generally low-level 'leakage'.
However, if the lamp is damaged, and the user is being protected against accidental contact with live parts, say after the rectifier, would the type AC RCD operate is perhaps another question?
However, if the lamp is damaged, and the user is being protected against accidental contact with live parts, say after the rectifier, would the type AC RCD operate is perhaps another question?
The RCD almost certainly will not trip, as the current drawn by the lamp will probably be less than what is required to trip a 30 mA RCD.

This 16 watt equivalent LED bulb draws 11 mA so it should not trip a 30 mA RCD.

This 40 watt equivalent LED bulb draws 25 mA so it will trip many 30 mA RCDs, but not all of them.

You have to remember, it’s not that long ago that electricians Voltage Testers had a replaceable light bulb in them, though not many are still in use.
When I started work many electricians had a small light bulb in a bulb holder wired to a couple of test leads for simple testing, but of course there was not any RCDs.

The equivalent modern LED Voltage Indicator draws <3.5mA, with switches depressed 28mA @ 240VAC, 60mA @ 500VAC
So should not trip an 30 mA RCD and unless the buttons are pressed to lower the impedance, but even then the 28 mA current may not be enough, that is the trip current for many 30 mA RCDs.

The equivalent modern LED Voltage Indicator draws <3.5mA, with switches depressed 28mA @ 240VAC, 60mA @ 500VAC
So should not trip an 30 mA RCD and unless the buttons are pressed to lower the impedance, but even then the 28 mA current may not be enough, that is the trip current for many 30 mA RCDs.