Adding up current

In a ring final circuit
(Based on Paul Cooks commentary of the 17th edition)

Very simple curent split using both legs of the ring

Not sure about adding up the currents in each leg
Take leg 2 Than will have the Ia of sockets 4,3 and 2
and the Ib of socket 1
How do these add up so you know the current in this leg?
Hope that makes sense
Thanks


Parents
  • Thank you very much

    OK thats what I was curious about if the currents cancel out.
    So leg three would have 3A clockwise and 3A anti clock wise, so no current as you say.

    I see my initial sketch was incorrect
     Leg 2 would have 5 amps

    CW 1A, 2A, 3A  and ACW 1A  so a total of 5A

    I will put together a more realistic sketch

  • John, I think that it may help if you have different loads at each socket. Try 4, 6, 8, and 10 A. The resistance of the cables is much lower than the loads, so that may be ignored.*

    It may also help to turn on one socket at a time. So 4 A at socket 1 would be 2 A acw in leg 1 and 2 A cw in legs 2 to 5. Etc.

    *ETA: my apologies - that is incorrect.

Reply
  • John, I think that it may help if you have different loads at each socket. Try 4, 6, 8, and 10 A. The resistance of the cables is much lower than the loads, so that may be ignored.*

    It may also help to turn on one socket at a time. So 4 A at socket 1 would be 2 A acw in leg 1 and 2 A cw in legs 2 to 5. Etc.

    *ETA: my apologies - that is incorrect.

Children
No Data