Upstream downstream RCD test

GN3 advises that the test should be conducted upstream neutral to downstream line. It would appear that there is a functional reason but I would like some clarification. Yesterday I used the method to test several Contactum RCBOs. As per GN3 method at x1, all operated between 14 and 18ms. Reversing the probes to upstream line and downstream neutral, all operated but the instrument reported greater than 300ms. 

Parents
  • The basic theory of operation of an RCD tester is that it applies the test current and starts a timer.

    Its stops the timer and displays the result when the voltage on the line test probe disappears (due to the RCD contacts opening) or the limit of the timer is reached.

    If you have your line test probe on the ‘upstream’ line terminal of the RCD then it will remain live after the RCD contacts have opened.

    The RCD tester therefore will continue to see voltage on the line test probe, the timer will reach its limit and the instrument will display an over-range indication (for example > 300 ms). 

  • A useful point.

    I had expectations of some subtle internal influence within the RCD itself (like those DC current - type AC vs A discussions)