Upstream downstream RCD test

GN3 advises that the test should be conducted upstream neutral to downstream line. It would appear that there is a functional reason but I would like some clarification. Yesterday I used the method to test several Contactum RCBOs. As per GN3 method at x1, all operated between 14 and 18ms. Reversing the probes to upstream line and downstream neutral, all operated but the instrument reported greater than 300ms. 

  • The basic theory of operation of an RCD tester is that it applies the test current and starts a timer.

    Its stops the timer and displays the result when the voltage on the line test probe disappears (due to the RCD contacts opening) or the limit of the timer is reached.

    If you have your line test probe on the ‘upstream’ line terminal of the RCD then it will remain live after the RCD contacts have opened.

    The RCD tester therefore will continue to see voltage on the line test probe, the timer will reach its limit and the instrument will display an over-range indication (for example > 300 ms). 

  • A useful point.

    I had expectations of some subtle internal influence within the RCD itself (like those DC current - type AC vs A discussions)

  • The RCD tester therefore will continue to see voltage

    not on a dual pole RCD ;) the opening of the neutral removes the supply to the tester as surely as opening the live would. However, the neutral break may be delayed after the live break, in 3 phase systems this avoids a load being strung between 2 phases, and in a single phase system it can still be used to allow a smaller contact and arc trap, as the main interruption occurs on contacts taking the live side. 300msec is rather long for that sort of delay however, and more like 10-20 ms is enough.

    Actually, ideally we'd measure for lost power between L and N on the load side of the RCD as that is what us being protected, and just introduce the fault between load side live and supply side neutral, as this is closest to emulating a live to earth fault.

    However a 2 pole tester is easier to understand and use,.
    Single pole breaking RCBOs need to be considered differently,. as here although the neutral side is sensed, it is never interrupted, so as suggested above, the device will trip, but the meter will time out. Mine stops after 2 seconds to spare setting fire to the fault path resistor.

    Are these single pole breaking RCBOs? 

    Mike.

  • Yes, single pole type A.

    Like Philip, I was expecting some explanation buried in electronics. Really good to know so thanks Ross and Mike. EDIALD!

  • GN3 advises that the test should be conducted upstream neutral to downstream line. It would appear that there is a functional reason but I would like some clarification. Yesterday I used the method to test several Contactum RCBOs. As per GN3 method at x1, all operated between 14 and 18ms. Reversing the probes to upstream line and downstream neutral, all operated but the instrument reported greater than 300ms. 

    PD IEC/TR 62350 simply says 'The testing current should be applied between the upstream and downstream terminal of the RCD.' and does not make a recommendation.

    However, there is a good reason to test to the upstream neutral for safety, being that after the test, at least in traditional unidirectional circuits, if successful, the outgoing (load-side) line conductor ought to be 'isolated' from the supply, and in TN systems at least, the upstream neutral ought to be well-earthed, so this hopefully leaves the test equipment in a relatively safe state. In the UK at least, there is not always a need to isolate the neutral in TN systems, and RCDs need not isolate the neutral for the purposes of protection against electric shock (i.e. conforming to Chapter 41 of BS 7671).

    In an IT system, especially one in which there is no impedance earthing, it wouldn't make much difference.

    If you have your line test probe on the ‘upstream’ line terminal of the RCD then it will remain live after the RCD contacts have opened.

    I'm not so sure this is correct for all testers ... because the test method is also valid (if the test equipment is so designed) for testing three-phase RCDs in systems with no neutral, where only a downstream and upstream line conductor are available. Guidance Note 3 says the following:

    An example of test instruments that follow (b) in the clip above from GN3, is the Megger 1730 and 1740 series that are rated for three-phase systems (I understand some models are only suitable for single-phase circuits) ... but other testers with equivalent features in this regard are available of course.

    Such approach does not leave the tester quite as safely 'isolated' so more caution is needed by the operator.

  • not on a dual pole RCD ;)

    Yes . . . a simplified explantion assuming a single-pole RCD . . . or indeed testing between the downstream line terminal of the RCD and earth, as is still the method shown in many instrument manufacturer's manuals. Slight smile

  • I'm not so sure this is correct for all testers ...

    The 'voltage' theory of operation is mentioned in one or more IET publications and is mentioned in a small number of instrument manufacturer's manuals, but in the latter case the instruments are for single-phase use only.

    An alternative (but related) theory of operation suitable for both single-phase and three-phase use may be the measurement of the time for which the test current flows, from application until current flow is terminated by the opening of the RCD contacts?

  • with a resistive test load emulating the fault, a detection of either the voltage across it or the current through it, both amount to the same thing, and the detection is also the same thing, namely at least one pole in the fault loop to be opened.

    Mike  

  • with a resistive test load emulating the fault, a detection of either the voltage across it or the current through it, both amount to the same thing

    Having just drawn a quick diagram, that has become apparent . . . that will teach me to consider such matters this late on a Sunday evening! Slight smile

  • with a resistive test load emulating the fault, a detection of either the voltage across it or the current through it, both amount to the same thing, and the detection is also the same thing, namely at least one pole in the fault loop to be opened.

    BUT ... the test equipment standard does include for earth potential rise for safety... now, whether this is to the 'cpc' line, or 'earth' from someone touching the instruments, is another perspective ... BUT GN3 does include the '3-wire test' options to account for the former, and in this respect   has a point ... and I apologise for not considering that with a complete explanation in my earlier response.

    But yes, this usually single-phase only tests.