Upstream downstream RCD test

GN3 advises that the test should be conducted upstream neutral to downstream line. It would appear that there is a functional reason but I would like some clarification. Yesterday I used the method to test several Contactum RCBOs. As per GN3 method at x1, all operated between 14 and 18ms. Reversing the probes to upstream line and downstream neutral, all operated but the instrument reported greater than 300ms. 

Parents
  • A single pole RCD device tested between the live input and neutral output should trip, but the tester would not know the RCD has tripped as it still has a live, neutral and earth connection, and there is no loss of voltage, hence no tripping time is recorded, despite the RCD having tripped.

    The up/down test allows a RCD to be tested without tripping another upfront RCD.