Upstream downstream RCD test

GN3 advises that the test should be conducted upstream neutral to downstream line. It would appear that there is a functional reason but I would like some clarification. Yesterday I used the method to test several Contactum RCBOs. As per GN3 method at x1, all operated between 14 and 18ms. Reversing the probes to upstream line and downstream neutral, all operated but the instrument reported greater than 300ms. 

Parents
  • The GN3 recommendation to test upstream neutral to downstream line reflects the RCBO’s internal sensing and tripping mechanism. Testing in the reverse direction can still cause the device to operate, but the measured trip time will not represent normal performance, as the current path differs from the intended sensing circuit. The observed >300 ms is consistent with this effect and does not indicate a fault.

  • Testing in the reverse direction can still cause the device to operate, but the measured trip time will not represent normal performance, as the current path differs from the intended sensing circuit.

    This could be the case for RCDs (particularly voltage-dependent devices) for use in TN and TT systems - although in general is this not confusing the positive and negative half-cycle applied tests (0° and  180°) with the 'polarity of the live terminals of the RCD'.

    But What about RCDs in IT systems, or separated systems?

    Particularly in IT systems, there's no saying which line (or if three-phase, one line or neutral) will become earthed ... meaning on the second fault (which provides the shock risk) the device is working 'neutral to line' ... so the RCD has to be able to operate 'upstream neutral to downstream line' and vice-versa?

  • Very relevant point. In IT systems, any conductor may become referenced to earth, so on the second fault the RCD must still trip regardless of line/neutral orientation. Residual current sensing is inherently non-directional, although voltage-dependent RCDs may still require correct supply connection for their electronics.

Reply
  • Very relevant point. In IT systems, any conductor may become referenced to earth, so on the second fault the RCD must still trip regardless of line/neutral orientation. Residual current sensing is inherently non-directional, although voltage-dependent RCDs may still require correct supply connection for their electronics.