Cable connection between the equipotential earth bonding bar (EBB) and the and distribution board

This follows on from a prior question and discussion: Cable size between equipotential earth bonding bar and distribution board in a Group 1 medical location

Regulation 710.415.2.3 states: The EBB shall be connected to the system earthing using a protective conductors having a cross-sectional area greater than or equal to the largest cross-sectional area of any conductor connected to the EBB.

Note HTM 06-01 provides no further definition of the point of connection of the EBB and the connection to the systems protective earth.

The clause is silent on the location; however, the consensus was:  the local Distribution Board  rather than the origin suffices.

Question 1 : The following statement has provided by a hospital engineer questioning this. Is this considered a user preference rather than regulatory compliance:

''Where practicable, medical equipotential bonding should be connected directly to the main earthing terminal to ensure integrity and clarity of the earthing system. 

 Risks of wiring EBB to a DB;

  •  Increased dependence on downstream connections
  • Higher chance of unnoticed disconnection
  • Harder inspection and fault tracing
  • Greater lifecycle risk
  • You are relying on the DB & MET connection
  • Any future alteration, loose termination, or undocumented change can ;Increase impedance/break the bonding path
  • The EBB is a safety reference, not just a CPC
  • Increased impedance & higher touch voltages under fault conditions
  • DBs are: Opened/modified/extended & re-terminated
  • During future works: Earth Bars get disturbed/conductors get moved or resized/Temporary disconnections occur
  • The medical equipotential system can be compromised without anyone realising
  • Parallel earth paths and circulating currents cause issues with testing

 Direct MET connection provides a solution that is as follows;

  • Lowest risk
  • Clearest compliance
  • Preferred by healthcare AEs on a new project 

Question 2 : From the statement above is this statement correct:  The EBB is a safety reference and not just a CPC

Parents
  • Are the diagrams in Fig 710.2 and 710.3 not illustrative of the requirements?

    If you don't connect the EBB and the medical IT system to the TN system earth:

    1. Won't they require their own independent earthing system, rather than providing the PE connection to Earth from the medical IT system through the mains earthing system?

    2. Won't you still need to bond the TN system to the EBB and equipotential bonding system in the location anyway to prevent touch voltage and meet the requirements of the equipotential bonding system for the location? Aren't more bonds between systems better at reducing impedances?

Reply
  • Are the diagrams in Fig 710.2 and 710.3 not illustrative of the requirements?

    If you don't connect the EBB and the medical IT system to the TN system earth:

    1. Won't they require their own independent earthing system, rather than providing the PE connection to Earth from the medical IT system through the mains earthing system?

    2. Won't you still need to bond the TN system to the EBB and equipotential bonding system in the location anyway to prevent touch voltage and meet the requirements of the equipotential bonding system for the location? Aren't more bonds between systems better at reducing impedances?