Is the interconnecting cable between outdoor and indoor AC units classed as a control cable or power cable?

Is the interconnecting cable between outdoor and indoor AC units classed as a control cable or power cable?

Parents
  • I suppose there is rather a precedent for the HVAC industry using SY ... even though many manufacturers labelling it as a control cable (although others have claimed at least part BS compliance).

    should comply with BS or harmonised standards

    OR ... IEC or the appropriate standard of another country (133.1.1) OR the designer confirms that it provides at least the same degree of safety (133.1.3) - so it's not quite a simple yes/no.

    Of course there's nothing stopping a control/auxiliary circuit running at full mains voltage (e.g. see fig 55.1)

       - Andy.

Reply
  • I suppose there is rather a precedent for the HVAC industry using SY ... even though many manufacturers labelling it as a control cable (although others have claimed at least part BS compliance).

    should comply with BS or harmonised standards

    OR ... IEC or the appropriate standard of another country (133.1.1) OR the designer confirms that it provides at least the same degree of safety (133.1.3) - so it's not quite a simple yes/no.

    Of course there's nothing stopping a control/auxiliary circuit running at full mains voltage (e.g. see fig 55.1)

       - Andy.

Children