Is the interconnecting cable between outdoor and indoor AC units classed as a control cable or power cable?
Is the interconnecting cable between outdoor and indoor AC units classed as a control cable or power cable?
Could be either ... or both.
It's certainly part of 'machinery' as defined in the Supply of Machinery (Safety) Regulations, and therefore not completely in the scope of BS 7671 ...
Not sure about that - there is no reason a competent person cannot install to the relevant machinery standard by following well written maker's instructions, which may need you to do things that are not be as simple as BS7671.
Actually we already see this with things like heating controller wiring and alarms and so on, where '7671 does not really cover the situation. As a very noddy example how would you test a Honeywell Y plan boiler installation to BS7671 ? Concepts like Zs go out of the window with 3 way valves stalled in mid position with diodes across micro-switches.Usually, as the boiler is considered an appliance, so you don't test the installation components, just the whole thing.
I believe it should be in scope of BS7671, as someone needs to certify it on install as compliant
Compliant with what? I agree with Graham, there seems little doubt that the cable is connecting two parts of a machine.
Let's suppose that your friendly local sparks installs a new circuit which terminates in an isolator. He (or she) notifies the new circuit to building control. That is BS 7671 sorted.
Householder then pops down to Screwfix and wires in the ACU. There may be a requirement to notify under another part of the building regulations, but that is not what we are talking about here.
Without some kind of entry in BS7671 it leave the engineering judgement open to the Designed and/or the Installer. Now let me put this question forward.
In the UK have you seen an AC unit with wiring outside using SY or CY cable? If so how will that cable deal with UV from the sun? Does the MI specifically forbid SY/CY cable outside and recommend/demand a HO5 or 7 variant?
wiring outside using SY or CY cable?
Plenty, and we use a lot of SY at work for voltages well above mains because of the RF shielding properties. Over a decade or so, if fully exposed to sun, and most is not, I'd expect SY failures at the clear jacket, and one can see the steel wires begin to rust where the outer has opened, and after perhaps another decade the shielding efficiency is lost. At that point it is pretty much as good as permanently installed arctic flex.
There is a lot of '7671compliant surface mounted and catenary slung twin and earth and arctic style PVC cable as well, that slowly embrittles, cracks and fails on a similar timescale.
As SY actually reveals it is failing, by the discoloration as the inner cores rust I personally like that inspectable quality. What I do not like is that almost no-one seems to have bothered to learn what to do with the braid in termination.
I think it is a bit silly and unfortunate that there is no BS recognised standard for SY and CY cables, but they have their place (out of the sun, ideally).
Mike.
recommend/demand a HO5 or 7 variant?
Be careful with those cable specs - H only means it's a harmonized type, 05 or 07 the voltage range - so nothing there specifies UV resistance at all.
- Andy.
recommend/demand a HO5 or 7 variant?
EG H07RN-F
H07RN-F cable is UV resistant and suitable for long-term outdoor use, including direct sunlight exposure. Its robust PCP (polychloroprene) sheath protects against environmental, chemical, and mechanical stresses, making it ideal for industrial, agricultural, and construction applications
Key features regarding durability include:
- Weather Resistance: Designed to withstand exposure to sunlight, moisture, and extreme temperatures (-30 - +60 degrees celcius).
- Structural Integrity: The UV-resistant outer sheath prevents the material from drying out, cracking, or bursting when exposed to sunlight.Versatility:
- It is oil-resistant and flexible, commonly used for connecting machinery, heavy-duty tools, and temporary power supplies in open air
Exactly my question, this specified by the manfacturer, which distribute the same equipment around the world, ive never seen this cable used in the UK for AC interconnections, but, this cable is not LSF so not suitable in some locations
To another point on the design of the machine, it's also a requirement to design the installation and certify it, along with conplying with the UK regulations
Might be wroth speaking with Doncaster Cables Technical team?
Tel 01302 821700
email sales@doncastercables.com
website. https://doncastercables.com
Might be wroth speaking with Doncaster Cables Technical team?
Tel 01302 821700
email sales@doncastercables.com
website. https://doncastercables.com