I am not an electrician but have a personal technical interest in understanding the Wiring Regulations.

I have become a bit confused by some contributions on the internet which seem to suggest that the adiabatic calculation will determine the size of CPC that will "cope with" a temperature rise to the maximum temperature permitted for a given cable type.

But as I understand it, it is the insulation which has to tolerate the temperature rise. This rise is caused by the heating effect (IsquaredR) of the current flowing in the CPC (and live conductor) under a dead short earth fault condition and which flows for the time it takes for the overcurrent protective device to disconnect the supply. Exceeding the maximum permitted temperature would permanently damage the insulation which I assume would no longer insulate.

Outside the parameters of the adiabatic conditions I assume that the conductors themselves could tolerate a very much higher and longer duration current, and hence temperature rise, before they themselves would become damaged. The only damage I can think of is that an unprotected conductor would melt like a fuse.

But for the adiabatic conditions of a known maximum level of earth fault current and a known OCPD disconnection time, the equation will determine the minimum size of CPC which would generate a temperature rise in the cable to the maximum permissible temperature for the insulation. In the case of a multi core cable like twin and earth, I assume that for an earth fault the heat contribution from the live conductor is not considered because the contribution from the smaller and hence higher resistance CPC will be much greater and more significant.

I will be pleased to hear from expert readers to confirm or otherwise clarify if I have understood the theory of this correctly . Thanks

  • But as I understand it, it is the insulation which has to tolerate the temperature rise.

    Well, more correctly, the cable as a whole, in its installed conditions ... if the cpc is a separate conductor, yes, the insulation, but if it's in a cable, it's the cable itself - which depends on whether the cpc is a conductor of the cable,  armour, outer conductor, etc.

    Outside the parameters of the adiabatic conditions I assume that the conductors themselves could tolerate a very much higher and longer duration current, and hence temperature rise, before they themselves would become damaged. The only damage I can think of is that an unprotected conductor would melt like a fuse.

    Hmmm ... that depends on the fault current and duration, and whether you want to take into account the adiabatic criterion, or take a non-adiabatic approach. All are covered in BS 7671, although generally courses only cover the faults of a very short duration, meaning the adiabatic is used.

    But for the adiabatic conditions of a known maximum level of earth fault current and a known OCPD disconnection time, the equation will determine the minimum size of CPC which would generate a temperature rise in the cable to the maximum permissible temperature for the insulation.

    For a fault of short duration.

    The big issue, is where the OCPD, and in particular a circuit-breaker, that operates in less than 0.1 s (as most do, for most faults), it's not the separate values of I and t that must be used, but the value of let-through energy (I2t) that is used in the formulas for both live conductors, and protective conductors.

  • The adiabatic equation assumes that the cable is heating up so fast that there's no time to dissipate any heat through the insulation.

    So it's not really considering the "contributions" of the live and CPC conductors. The two are separate.

    The CPC is thinner so it has both a higher resistance and lower thermal mass. So it will overheat faster than the live.

  • The problem is not vaporization or fusing of the copper, it is more if the cable is fit for continued service after the fuse or circuit breaker has operated after a 'worst case' fault.

    Fusing the conductors requires  many orders of magnitude more energy. Its also why current ratings for example for mineral insulated wires are noticeably  higher than PVC or polyethylene for the same copper cross-section.. 

    Considering 'not fit' for use, for example have the heated cores moved in the plastic (think hot wire cutter like) or has the insulation near the copper been converted to a conductive char, or in some other way decomposed or made brittle ? 

    The calculation is one of a maximum credible temperature rise during the time the fault current flows, and assumes the only thermal absorber is the metal itself, and that no energy is lost into the environment or into the bulk insulation,  and because some energy always is, the adiabatic approximation is always a slight over-estimate - that is to say that  a bit more current is OK.

    Mike.

  • But as I understand it, it is the insulation which has to tolerate the temperature rise. 

    Correct (the consideration is not just for the metallic conductor alone but also what's around it that sets the limit on acceptable temperature rise) - and that requirement is captured in the differing values for "k" (as per tables 54.2 to 54.6)

    The only damage I can think of is that an unprotected conductor would melt like a fuse.

    Or thermally damage the supports (think bare bus-bars) or even damage to the conductor's surroundings - e.g. setting fire to adjacent materials.

       - Andy.

  • Thank you @gkenyon, @Simon Barker, @mapj1 and @AJJewsbury for your feedback. 

    I'm digesting your comments and studying a bit more before I ask any further questions about them.

    In the meantime thanks

  • Mean while, although no figures  for hot bare copper, are in the wiring regs BS7671 it is interesting to look at the figures the ENA use for DNO type wiring at substations.
    Bare strips and bare stranded wire can be  used for earth bond interconnections to electrodes and between enclosures & so on.

      This table suggests that the  (smallest )bare copper 70mm2 cable is good for at least 8000  amp faults  for 3 seconds, but there is no insulation to damage. Note that at the end of the 3 seconds, the copper is at 405C - a temperature that would be put any kind of plastic insulation beyond use. The same document recommends no more than   325C for aluminium cored wire, and 400C for galvanized steel parts and a 250C rise for exposed bolted contacts however,...

    These are far higher fault current ratings than 'normal' can only be safely used when there is no part in contact that would be damaged by the heat. In a controlled location like a substation this is practical , as only competent persons are installing things, and the dangerous bits are in a locked compound or box, but even so if it were much hotter it would  leave scope to set fire to leaves, dust  or cobwebs, and as it is there are considerations of thermal expansion and stress on joints - hence the reduced limit on bolted connections  !.

    ref https://www.ena-eng.org/ENA-Docs/D0C3D1R/TS_41-24_181106101835.pdf
    regards Mike

  • I'm still studying about the adiabatic equation and in so doing I've learned a bit more about the way the K factors which appear in the regs have been calculated. This is a level of detail a bit removed from my original query but is all adding to my understanding.
    I found an old entry of yours (screenshot) giving the formula used. I wrote this out on two sheets of paper (attached) and sure enough it works. I used the case of thermoplastic pvc rising from 70 to 160 degrees, k=115
    I'm still studying just to satisfy my technical curiosity but for the moment the derivation of the formula and some of the parameters used (e.g. the reciprocal of the temperature coefficient) is beyond my existing knowledge of the physics.
    I'll return to my original query when I've got my thoughts together 
    Thanks to all respondents 
  • Sorry forgot to rotate the scan

  • How nice to see some proper scribbling! :-)

  • Indeed.

    It may help to consider the example of  a particular cable size, say 2.5mm2 and do a 'no text book' estimate.

    First the no of grams of copper in a 1m length of that cable  which is 2500 cubic mm, or 2.5 cc at  about 9 grams per cc so 22.5 grams) and the electrical resistance of that 1m length (about 7,5 milliohms).

    And there you have all the bits you need.  

    The energy to raise 1 gram of copper through  1 degree is about 0.38 joules, so to raise 1 gram of  it by 90C is 34Joules or 34 watt seconds. but of course we have 22,5 grams, so 760 watt seconds for that 70C to 160C rise. 

    Note that watts /R has the units of I2t.

    760 /0.0075 ~ 100,000. 

    Note he book value is normally taken as 77,000 so we are about 20%  out, but there has been some pretty casual rounding and we have nor allowed for the resistance rising when hot. 

    However, this is the same approach, just with all the steps showing.

    Mike.