USB charger outlet in Bathroom Zone2
I've been asked to add a USB charging port into a bedroom with a bath in it.
My understanding of BS7671 is that a room with a bath is a bathroom. As such the outlet would be in zone 2 of the bath.
Would I need to power the charger via a safety transformer and could this be built into a +IP4 enclosure similar to a shaver outlet
Thanks for your assistance
  • but fittings like this are not supposed to supply more than one hand held appliance at a time
    I suppose it depends if the USB and shaver sockets are galvanically connected - if not you'll end up with, in effect, two separate system that just happen to share a plastic box - so no real risk there (if they are indeed separate).
  • I presume there are no restrictions  once outside zone 2 but  not the full 3m away from zone 1?
    It's 2.5m these days rather than 3m, but yes the limitation is on all sockets except SELV or isolated shaver types. 701 specific requirements for the room/location outside zone would still potentially apply (e.g. connected to supplementary bonding system if there is one, if the output was PELV for instance, RCD additional protection etc.)
  • my cardiologist doesnt recommend this as teeth have a nerve pathway to the heart and pp3 have cause arrhythmia
    oof; A reference would be useful, if available, for my/folk's files.
    The PP3 does have its return path close to the source connection. Looping the contact between tongue and [wet] toe may be too exciting Grimacing
  • The only sensation I or others I deal with feel is the catheter moving around.
    Interesting. I didn't feel it at all.
  • Other transplant and ICD patients.
    I've have no research or verified data just about 50people and 1 cardiologist's statement
    Correct, although as in the electric shock case I pointed to, people will use long leads if they are hell-bent on charging in the bath ... although assuming there are mains socket-outlets in the bathroom, you wouldn't be making things any more dangerous.
    For the avoidance of doubt, according to the electronic product manufacturers, using devices on charge in the bath is misuse ... I'm not saying manufacturers are doing anything wrong, nor am I saying installers are in the wrong for putting socket-outlets or charging equipment in compliant places that might make use of USB charging for devices in a bath more accessible.
    The problem I have is, at what point does it become 'foreseeable misuse' from the perspective of a court ? What, if anything, can we do in our standards and practices to prevent that misuse?
  • although as in the electric shock case I pointed to, people will use long leads if they are hell-bent on charging in the bath
    If you bring an extension lead in from the landing, the door will not be locked (unless there is a gap beneath it). There is case-law concerning deaf people, fire alarms, and entitlement to personal independence payment which is based upon the notion of bathing privately.
    That said, if you bathe in a bedroom, presumably privacy is not at the top of the agenda, particularly if you are Whatsapping at the same time.
    Judges in the Appellate Courts seem to have taken a common sense approach based upon the facts. This thread is evidence that some people do take a 'phone (or iPad or WHY) into a bath whilst it is charging, so I am not sure that foreseeability is the issue.
    I suspect it really is a matter of where the duty of care lies. Is it the manufacturer or supplier of the 'phone, the manufacturer or supplier of the extension lead, the electricity supplier, BSI, and so on?
    My personal opinion is that a warning in the instructions discharges the duty of care.
  • My personal opinion is that a warning in the instructions discharges the duty of care.
    I wouldn't disagree with that .. although there are ways in which changes have been sort of mandated in product standards; for example, the safety interlocking system that requires a start button to be pressed to restart a domestic tumble dryer to prevent the machine automatically restarting if a toddler gets in and the door shuts.
    (Surely children ought to be supervised, though?)
  • This is why I would limit USB output to the fixed low voltage of 5v. I would be supplying to a contractor who is supplying to the prime contractor who is fitting it to hotels. Any warning would need to be added to the front plate in all languages (person in bath crossed through icon?).
    But looking at the risk to all involved limiting voltage to 12v max, separated from earth with a max output in fault condition of 20va (as per shaver) limits the risk to life.
    My research would suggest the risk even with bath salts and damaged skin to negligible although the USB probably wont charge many new devices. Therefore whats the point?
    I have to be honest, I still cant see how a floating voltage between + & - so close together offers any risk given that pin to pin must sill be the shortest and lowest resistance path. I dont understand why the electrons would go the lone way round and even into the wet human body even at only 500ohms resistance that achieves enough to reach let go levels let alone death.
    This is way below hospital limits
  • Surely children ought to be supervised, though?
    Parents of young children need eyes in the back of their heads.
    Doesn't help if a cat sneeks in - link. What a beauty!