230V Supply from 400V Line to Line in a Control panel

Hi, 


I have a situation where I need to install a 230V control system which draws about Max 5A ( at230V) inside a existing Dinrail enclosure. 
However, the incoming (feeder) cable of this enclosure is a 3 Core + Earth and doesn't have a Neutral, as the load is 3 phase with no neutral.

My task is to provide a 230V supply for a control equipment that we are going to install inside this enclosure. I am struggling as there is no neutral available. 
feeder is very long hence we cannot afford to run a neutral from the SDB to this enclosure.  either. 

1) Would it be possible to mount a small control transformer and feed this with 400V supply and then generate a 230V supply ? (below link)

https://www.yesss.co.uk/eris-400va-panel-transformer-230400v-primary-122448110240v-secondary?srsltid=AfmBOoq0MCaJYskcQovSxGEfzGITtVWGUpqrmsWnTT7WLwGIsOa1xMz0


2) and if so, will this be a floating neutral ? and how do I make the neutral 0V then if required? from a practical point of view.

Thank you in advance for your support. 

Parents Reply
  • Will the 5A at 230V significantly 'unbalance' the three phase, pushing problems back up the line?

    It'll have unequal currents, but will still be balanced (in the sense that the vector sum of L1 L2 and L3 will still be zero) - much like the DNO's HV system where a single phase transformer is hung underneath a 3-wire 3-phase system.

       - Andy.