Micc or FP200 cable in chapels or churches ?
Hello, looking for an answer to who decides if a chapel / church needs to wired in MICC cable or will FP200 be adequate ? I appreciate it should be fire resistant and MICC is smaller and looks great if installed properly , but I cant find any guidance anywhere
  • Thanks
  • When I design rewires in listed Church buildings if it's surface I'll specify bare MICC and any cables not in public view FP200, all designs have to be cleared by the Diocese DAC panel and they will accept / reject your proposals.
  • I have a question, on MICC in Churches - Life expectancy.
    I first met Pyro, MICC cable, 57 years ago, on a steelworks student placement job (three conductors about 10mm d, per phase), but I went into Telecommunications. I visited the BICC factory nearly 40 years ago, in connection with zero halogen twisted pair MICC, but that factory is now closed. And I have done a few minor MICC installations and repairs.
    So I know MICC is good stuff and copper water pipes pretty well go on for ever.
    Our local Church was rewired in Pyro in 1966, and the majority of circuits are the lighting circuits, which were designed for ES 200W tungsten gls, and are now being changed over from 55W CFL to 24W ES led lamps, so the load requirement has reduced. There is no evidence of damp causing verdigris, except in one short location. It was installed by Engineers within the congregation who dried the cable ends, before terminating, to a greater degree than the Pyro specification.
    The Church is planning to probably upgrade the heating from gas boilers to a heat pump, consequently would require a supply upgrade.
    The Rector has said that as we are having some electrical work done, "should we have the whole building rewired?", knowing that traditional VIR wiring has had to be replaced at an earlier age.
    My gut feeling is that Pyro could last hundreds of years, but I need some evidence of older installations, still working.
    I have come across a reference to a 70 year old installation, but that is only 10 years on from where we are now, to get that far. The routine testing does show good IR results, so I am trying to find a somewhat older figure, to show ours could keep going, for a longer time.
    I have heard of one military boiler house installation that had a failure, the caretaker polished the copper sheath, and after many decades, wore it away and damp got into the insulation so it failed.
    Has anyone out there met any Pyro / MICC installations of a good age preferably nearer, or more than 80 years and still in excellent condition? I would like to hear about the longest.
    Who can come up with the oldest?
    Where we have a bit of verdigris, should I slide a bit of thin plastic between the cable and stonework, and perhaps apply clear varnish?
    Many thanks
    Andrew P. Jones
  • well amusingly, pyro (mineral insulated cable) is the only thing on this list of Raychem products that attracts a 'lifetime' warrenty.
     https://pim.chemelex.com/Product%20Documents/Warranties/RAYCHEM-WS-H57397-LimitedWarrantyExtNAMLATAM-EN.pdf?
    The rest seem to be 5,10 or 20 years. Faults due to poor installation is not covered..
    to compare https://uk.prysmian.com/media/news/cable-design.
    Prysmian reckon 25 years for the sort of plastic covered cables we are more familiar with.
    I'd be disappointed if it failed after twice that in benign conditions - even the twin and earth in my place is older than that and doing fine.
  • Not my area, but what are the failure/repair mechanisms, and would a 'run to failure' / 'pre-placed repair kit' make useful sense?
    Or would failures in place be 'high consequence' (as opposed to cables being over stone work with low fire/incident risk)
    In the good old days one would have fuse wire ready at the fuse board,...
  • Prysmian reckon 25 years for the sort o plastic covered cables we are more familiar with.
    Mine is 44 years old.
    Buildings are not permanent structures. I discovered recently that UPVC windows, etc. have an expected lifespan of 35 years, which seems about right. More astonishingly, the lifespan of whole buildings could be as little as 30 years link.
    Even if buildings do last longer, if this parish is anything to go by, houses tend to get extensive refurbishments every 40 - 50 years. The church, which is only 92 years old had fairly extensive repairs about 5 years ago. The original vicarage, which was a little older, lasted about 80 years.
    According to Wikipedia (so it must be true), Pyrotenax started production in 1937. Given that not much would have been installed until after WW2, I doubt that you will find any installations which are more than 80 years old.
    In answer to the Rector's question, I would say that if it ain't bust, don't fix it. If somebody else asks the same question in 20 years, you may be able to give the answer. :-)
  • I reckon MICC cable of itself is pretty much non-aging - but the bits around it that are the weak points. Corrosion or imperfectly installed seals can let moisture in (but your decent IR measurements seem to cover that) - also the sleeving used on the cores at terminations was generally rubber or plastic of some kind - which is likely more liable to ageing than the cable itself - but a bit of inspection might be able to put your mind at rest on that score (the sleeving might even be replaceable while leaving the intact, depending on the detail of the seals).
    MICC sheaths typically form a massively oversized c.p.c. - which gives some significant safety advantages which would be unlikely to be matched by alterative multicore cable types.
    As well as the financial costs of unnecessary replacement, many organisations these days look at the environmental impact - even if all the copper is recycled the energy needed to melt it down alone would be significant. Far better to re-use (or just keep using),
  • I have recently been asked to estimate for a supply in a church for a door entry system. FP200 has been specified by the church for this new system.
    Alf.
  • In a rat/mouse attack on FP200 or M.I.C.C. I would put mu money on the M.I.C.C. any time.
  • Depends on which end of the rodent is causing the problem - against teeth for sure the copper will stand up better than a plastic sheath, if it's along a run and the creatures are forever leaving "bio bi-products" top of it, maybe the plastic might survive longer?