32A RCBO for sockets in industrial setting

i have a customer who has 32A sockets on an injection moulding machine. They are protected by RCBO, however, due to the heating controllers that get plugged in, they pretty much trip as soon as the heats are turned on. This means they then have to plug the box in to an older machine next door which is protected by MCB. Am i right in thinking that with the correct Risk Assessment that the RCBO could be swapped out for an MCB? Any advice greatly appreciated.

Parents
  • That would suggest a fault in the machine to me,unless the equipment manufacturer states it has a high protective conductor current,is this class 1 equipment?

Reply
  • That would suggest a fault in the machine to me,unless the equipment manufacturer states it has a high protective conductor current,is this class 1 equipment?