32A RCBO for sockets in industrial setting

i have a customer who has 32A sockets on an injection moulding machine. They are protected by RCBO, however, due to the heating controllers that get plugged in, they pretty much trip as soon as the heats are turned on. This means they then have to plug the box in to an older machine next door which is protected by MCB. Am i right in thinking that with the correct Risk Assessment that the RCBO could be swapped out for an MCB? Any advice greatly appreciated.

Parents
  • You may be able to take advantage of the exception in 411.3.3, but only if the equipment is used by instructed or skilled personnel. Note 1 is important.

    This changed with Amd 2.

Reply
  • You may be able to take advantage of the exception in 411.3.3, but only if the equipment is used by instructed or skilled personnel. Note 1 is important.

    This changed with Amd 2.