32A RCBO for sockets in industrial setting

i have a customer who has 32A sockets on an injection moulding machine. They are protected by RCBO, however, due to the heating controllers that get plugged in, they pretty much trip as soon as the heats are turned on. This means they then have to plug the box in to an older machine next door which is protected by MCB. Am i right in thinking that with the correct Risk Assessment that the RCBO could be swapped out for an MCB? Any advice greatly appreciated.

Parents
  • If these are mineral insulated heating elements it may be normal, but it may be an early warning of an insulation failure.

    It may be worth checking the heaters.

    The RCD may be omitted if the cable routes do not require RCD protection, being visible or in conduit or SWA etc and 

    1) the machine was hard wired, or

    2) if the socket was 63A or above, and  or where ordinary persons do not use it, and there is a documented reason and RA that describes how the risk is mitigated to an equivalent level by other means. It is very clear that is not the preferred route, although of course with older kit and older situations it is quite a common situation.

    generally, additional protection by an RCD not exceeding 30 mA is required, 

    1. Socket-outlets with a rated current not exceeding 32 A in locations where they are liable to be used by persons of capability BA1, BA3 or children (BA2, BA3)

    2. Socket-outlets with a rated current not exceeding 32 A in other locations

    3. Mobile equipment with a rated current not exceeding 32 A for use outdoors

    There is now no mention of a domestic caveat, as all installations are treated the same, and the socket-outlet rated current has increased to 32 A, from 20 A.

    The key part is that where any BA1, BA2 or BA3 persons are liable to use any such socket-outlets. These capability identifiers are as follows:

    BA1 – Ordinary person (non-electrically skilled or instructed)

    BA2 – Children

    BA3 – Disabled persons

    These categories are external influences, and a full description of them and other influences that may affect an electrical installation can be found in Appendix 5 of BS 7671:2018+A2:2022.

    Can we still omit RCDs?

    We can still omit an RCD, but only for indent (2); however, there must be a risk assessment for each socket-outlet that is to be omitted from RCD protection. Any risk assessment must be fit for purpose and adequate for the individual installation and its use. It’s for this reason the Client, duty-holder or user of the installation carries out any such risk assessment.

    Mike

  • Sorry, that  overlapped with other replies, but I think we are broadly on the same page.

    Mike