32A RCBO for sockets in industrial setting

i have a customer who has 32A sockets on an injection moulding machine. They are protected by RCBO, however, due to the heating controllers that get plugged in, they pretty much trip as soon as the heats are turned on. This means they then have to plug the box in to an older machine next door which is protected by MCB. Am i right in thinking that with the correct Risk Assessment that the RCBO could be swapped out for an MCB? Any advice greatly appreciated.

Parents
  • IET Guidance Note 5 Protection against electric shock provides some insight into how to deal with:

    (a) At Section 12.4.5, high protective conductor currents so that socket-outlets can be protected by 30 mA RCDs. Particularly, this equipment is machinery as defined in the Supply of Machinery (Safety) Regulations, and the method outlined in 12.4.5(c) of Guidance Note 5 is actually included in the relevant product standard (Clause 8.3 of BS EN 60204-1:2018+A1:2025). Ususally, where machinery has high protective conductor currents, suitable labelling and instructions are provided by the manufacturer according to Section 8.2 of BS EN 60204-1:2018+A1:2025.

    (b) At Section 12.4.3, risk assessments for omission of 30 mA RCD protection. In this, case, you might be able to weigh up whether risks in maintenance are increased by 'hard wiring' to a fixed switch-disconnector, rather than connecting via plug and socket-outlet ... but importantly, you will need to include the relevant dutyholder in the risk assessment.

    BS 7671 does permit 'hard-wiring'; to switch-disconnectors, though ...

Reply
  • IET Guidance Note 5 Protection against electric shock provides some insight into how to deal with:

    (a) At Section 12.4.5, high protective conductor currents so that socket-outlets can be protected by 30 mA RCDs. Particularly, this equipment is machinery as defined in the Supply of Machinery (Safety) Regulations, and the method outlined in 12.4.5(c) of Guidance Note 5 is actually included in the relevant product standard (Clause 8.3 of BS EN 60204-1:2018+A1:2025). Ususally, where machinery has high protective conductor currents, suitable labelling and instructions are provided by the manufacturer according to Section 8.2 of BS EN 60204-1:2018+A1:2025.

    (b) At Section 12.4.3, risk assessments for omission of 30 mA RCD protection. In this, case, you might be able to weigh up whether risks in maintenance are increased by 'hard wiring' to a fixed switch-disconnector, rather than connecting via plug and socket-outlet ... but importantly, you will need to include the relevant dutyholder in the risk assessment.

    BS 7671 does permit 'hard-wiring'; to switch-disconnectors, though ...