32A RCBO for sockets in industrial setting
i have a customer who has 32A sockets on an injection moulding machine. They are protected by RCBO, however, due to the heating controllers that get plugged in, they pretty much trip as soon as the heats are turned on. This means they then have to plug the box in to an older machine next door which is protected by MCB. Am i right in thinking that with the correct Risk Assessment that the RCBO could be swapped out for an MCB? Any advice greatly appreciated.
  • b) At Section 12.4.3, risk assessments for omission of 30 mA RCD protection. In this, case, you might be able to weigh up whether risks in maintenance are increased by 'hard wiring' to a fixed switch-disconnector, rather than connecting via plug and socket-outlet ... but importantly, you will need to include the relevant dutyholder in the risk assessment.
    In certain situations, perhaps like this one, inclusion of an RCD would likely introduce a greater risk. Motor swap out can be done easily, efficiently and safely to allow minimal downtime for this dockside unloading arrangement.
  • I wrote a reply that the software seems to have lost, here is another go.
    According to notifications, there was moderator activity around then. Apparently approved, but not appeared!
  • That is an example where there is so much interconnected steel that the earth connection is unlikely to be totally lost due to a simple break in a lead to  the  plug  ;-)   I'd argue the shock risk from a CPC fault is probably mitigated by the chassis acting as an auxiliary protective bond.. (are they only 32Amps?) the general construction is reminiscent of some fairground stuff.
    I'm also not sure that it is easily touched by children, elderly or even ordinary persons. Mind you, it is outdoors, but not really mobile.. I might worry about the dangling plugs filing with a mix of water and coal dust or whatever that is in the  background , mind you that would probably boil off pretty fast.
    You have some fascinating photos, where on earth do you find these things  ?!
    M.
  • You have some fascinating photos, where on earth do you find these things  ?!
    They are all from our own inspection activities. I often show them during my 2391 classes when we discuss the utter subjectivity of coding outside the domestic side of things, which is generally well addressed in Best Practice Guide 4. Always good for lively discussion!