TN-C-S (PNB) versus TN-C-S (PME).
How good are you at telling the difference?
  • My understanding is that the TN-C-S(PNB) earthing arrangement is installed by the DNO to provide a minimum of 8.000 metres separation between the transformer HV earth system and LV earthing system provided for the customer by the DNO.
    Agreed ... but there are two variations
     - one in which the system is earthed at one point only (at or before the first customer, typically of a maximum of 4 customers). This, however, is still NOT TN-S.
     - one in which the system is earthed at or close to each customer's premises (again typically no more than 4 customers). In this case, the N-PE siplt is often at the customer's premises.
  • Whilst one variant of PNB is closer to TN-S than PME, I'm sure it's not correct to term it 'TN-S'.
    TN-C and TN-C-S systems come in more variants than 'PME'
    From my occasional gazing at rural distribution systems I think it's quite common to have the (first) LV earth "one span" away from the transformer - as with HV overheads (what we used to call "hot" sites) the LV earth needs to be kept separate from HV earth regardless. I'm sure I've seen it on what must be PME on the LV side (as it feeds >>4 customers).
    My understanding was PNB was used where there really wasn't really the space to have multiple electrodes on the LV side (e.g. one span away from the transformer is the house). Of course it then gets extended when another house gets built next door... then it gets a lot messier.
  • I'm sure I've seen it on what must be PME on the LV side (as it feeds >>4 customers).
    Agreed, that would normally be done to full PME requirements.
  • My understanding was PNB was used where there really wasn't really the space to have multiple electrodes on the LV side (e.g. one span away from the transformer is the house). Of course it then gets extended when another house gets built next door... then it gets a lot messier.
    The original purpose was where there's pole-mounted transformer (HV to LV), and the transformer's HV earth is at the pole. Under these circumstances, it's rare that the conditions to combine HV and LV earths are met, so the LV earth has to be separated from the HV earth according to the relevant standards (see BS EN IEC 61936-1 and BS EN 50522 for the relevant conditions and requirements). Typically, as   stated, the separation distance between HV and LV electrodes is at least 8 m.
  • Typically, as   stated, the separation distance between HV and LV electrodes is at least 8 m.
    Who? Not me, Gov.
    However, Stepdaughter's previous semi-detached cottage is supplied from a pole transformer, which appears to be earthed on the LV side a few metres away.
    The supply is 2-wire aerial. It may at one time have supplied just the one house on that side of the road, but at some stage, the barn was split off to became in due course Stepdaughter's house.
    Exactly!
    The thing is that the service head has a PME link, but there appears to be no further earth. The lines do continue where they supply lighting down a private drive, but with no obvious distant earth.
    They now live adjacent to the field with the transformer, but the supply is underground - God knows what lurks there! In any event, the service head has a N-PE link. I know 'cos I have seen it.
  • Who? Not me, Gov.
    Sorry, it was   Grin
    Wouldn't mind, but I've not even had a beer or glass of wine yet !
  • The thing is that the service head has a PME link, but there appears to be no further earth. The lines do continue where they supply lighting down a private drive, but with no obvious distant earth.
    So the point here, is that if the second property has extraneous-conductive-parts, the neutral is now effectively multiple-earthed. It's still probably not PME, but it's certainly not TN-S either.
    My sister's house is similar ... it has a DNO-provided earth electrode, but I don't think they maintain that?
  • Overhead ABC supplying 460 volt splitphase with an unused core terminated into a three-phase DNO fused intake with TT earthing.
  • Pedantic question:
    an Earthing function
    What is an earthing 'function'?
    Is it a partial or complete function; a physical or conceptual item; is it extensive or point like ?
    I.e. Can this single connection be the complete earthing function, or are we "looking for the wires, not the electricity" (*) ?
    (*) the phrase was from a BBC interview with E.Powell about whether he was a power broker in politics.