Bathroom appliance help please
Hi guys just after a bit of advice here please
Customer wants to build a full height cupboard and the bottom of the bath and put a washing machine and tumble dryer in it. It will have a door on the cupboard.
How would regs apply to this ? I can make it 3 x flex outlets and sfs outside the bathroom if need be rather than sockets.
The appliances would technically be within 600mm from the edge of the bath but inside a cupboard so couldn't remember if that then meant zones did not apply
Thank you for any help here
  • Doors (together with walls, floors, fixed partitions etc.) do count 'where those effectively limit the extent of the location' - and traditionally the airing cupboard door was considered effective - otherwise the traditional DP switch for the immersion heater wouldn't have been been possible.
    There is still perhaps the question whether the door is 'effective' in limiting the location in your particular case - if it were a full height door hinged on the bath side for instance (so it was >600mm to go around it (like the 0.6m-S bits on the diagrams) that might be more reassuring
    Don't forget the general suitability for the environment though - high humidity, likelihood of condensation etc will still need to be taken into account.
  • If it was all rather more than 600m from the edge, and there was no socket within 2.5m, or as in this case a fixed outlet so no socket at all, , there would be no regs compliance questions.
    However, even then it might be unwise, for reasons of  damp and perhaps machines rusting away. Within 600mm, and you are on more dodgy ground, unless the machine makers actually say it is permitted.
    This is not so much about reaching with outstretched arms or dropping a portable thing into the tub. - that's the basis of the 2.5m rule,  but more about IP ratings and actually getting water poured on the kit from a misdirected shower head or a particularly splashy bather - think children playing...
    It might be possible to eliminate that risk  that with some sort of fixed screen, and good ventilation but I can imagine  any normal MDF or chipboard type cupboard getting pretty damp and mouldy unless very careful, and  the machine rusting merrily after a few years in a poorly ventilated wet space . If you could increase the distance, that would be preferred. (I have seem machines stacked one above the other (dryer on top shelf ) to do that but its not trivial cabinet work.)
    I would be a little careful here.
    In the CENELEC Harmonized Document HD 60364-7-701 that is likely to make its way into BS 7671 at the next version, the zones extend 60 mm into walls and partitions etc. surrounding the zones.
  • However, even then it might be unwise, for reasons of  damp and perhaps machines rusting away.
    At one time, I would have supported this perspective, and certainly up to the early 1980s, many machines on the UK market didn't do well in a bathroom environment.
    However, in today's global market, things are a little different.
    Many countries in Europe think having dirty laundry in the kitchen is quite disgusting, and bathrooms are a common place to find washing machines and tumble dryers. Machines are therefore now made with that use case in mind, it being relatively common in the European market at a whole.
    Also, I hope many bathrooms today are better-ventilated than those in the 1970s, or can be made so quite easily (if one has the correct certification to do that work, of course).
  • Many countries in Europe think having dirty laundry in the kitchen is quite disgusting, and bathrooms are a common place to find washing machines and tumble dryers. Machines are therefore now made with that use case in mind, it being relatively common in the European market at a whole.
    Personally I'd love to have my washing machine and tumble drier in the bathroom (if it was big enough) but at the moment the washing machine is in the kitchen and my tumble dryer lives in my shed face with hand over mouth
  • UK washing machines and UK tumble dryers are not designed for use in UK bathrooms which contain a bath and/or shower.  They will rust very quickly and internal parts will fail quicker.  There is also the very IMPORTANT point of a 230v nominal electrical item in a humid/damp environment which is unsafe even if a correctly selected and correctly functional RCBO (Type A minimum) is present.
    The most viable option in the UK for location of washing machine/tumble dryer outside of a kitchen/utility room would be a WC (Water Closet).  As always there are caveats
    Size of room
    Ventilation/Humidity extraction
    Power supply to the room with RCBO Type A minimum
    Splash protection from basin
    Water supply with an isolation valve and a non-return/double check valve
    Some may require a surge arrestor (often called a water hammer arrestor)
    Hopefully most people already have a water supply and waste management in the WC.
  • Also worth remembering that In countries like Germany, Type AC RCDs and RCBOs (which only detect pure sinusoidal AC fault currents) were officially deprecated for general human protection against electrical shocks in 1987.  Thus can we really use the full extent of Harmonized Document in the UK or do we just interpret and implement the intent of said Harmonized Document?
  • environment which is unsafe
    230V need not be unsafe in bathrooms, - and  if you travel to the continent you will see normal French and Schucko style sockets in bathrooms for hairdryers shavers and toothbrush chargers, and their accident figures bear out this is no more dangerous.  Generally though bathrooms are bigger - after all it leaves room for the washing machine to be that bit further from the edge of the shower tray or bath tub !
    I agree it needs some thought and wiring maybe a problem if done willy nilly, but its not unsafe if done properly
    That will be interesting -unless there are some caveats for thin walls.. For owners of 'park homes' i.,e static caravans, that makes the wall in another room that backs onto the bathroom a no- go area for wiring, as the walls may be only 50mm thick. It will be bad enough for those oil crisis era 1970s homes where the internal wall  blockwork is 75mm built on the floorboards - surface pattreses only perhaps
    Still made actually and sold for for internal walls, need a bit more skill to lay than the more common 100mm ones
    https://buildingshop.co.uk/product/aerated-blocks-standard-3-6n-75mm-thermalite-celcon/
    "Versatile Applications: Perfect for both load-bearing and non-load-bearing walls, infill panels, and various renovation projects. The 75mm thickness is commonly used for internal partitions and inner leaves where space and thermal value are key considerations."
    Funny, as I'm sure in my house, which has a lot of them, the main factor for the builder's decision was 'cheaper', but they don't mention that at all in the blurb !
    It 's already a pain if you need a 50mm back box for a cooker or something, you need to be very careful not to come right through.
  • Maybe but be carfeul with that - it does not mean that is what is installed, even now there are plenty of flats in Berlin that still have the Neozed/ Diazed  bottle fuses on a 16 or 32A 3 phase supply and no RCD at all. One of the unintended consequences of over regulating who is allowed to do rewires and upgrades is that it makes things more expensive and then it tends not to actually happen.
  •  Countries like Germany, Type AC RCDs and RCBOs (which only detect pure sinusoidal AC fault currents) were officially deprecated for general human protection against electrical shocks in 1987.  Thus can we really use the full extent of Harmonized Document in the UK or do we just interpret and implement the intent of said Harmonized Document?