Calibration of Approved Voltage Indicators and Proving Units.

There was an old discussion on this 7 years ago but it is locked now. In any case there was no definitive answer provided at the time. In years gone by, I would have thought that AVIs and PUs either work or they dont.

But searching online today, Martindale recommend that their AVI's and PU's do need calibrating. This has prompted me to rethink and I note that in GS38 point 30 talks about all test equipment being maintained by a competent person and one of the common errors being failing to verify correct function of illumination (eg indicator/lamp/neon).

If something were to go wrong, and it turns out the AVI and PU were not calibrated within the last 12 months, I can imagine this wording above being used to attribute blame to the person who was undertaking the proving dead.

When we prove the AVI with the PU, we are putting voltage onto the AVI and simply seeing that the lamps light up, but the PU just puts out the max voltage it is capable of, it doesnt step up or down each voltage level individually, so we dont control the level it is proving at. 

What's other peoples thoughts? I am considering now that we do need to calibrate these items.

Parents
  • My voltage indicators get checked every time on my proving unit, and also weekly on the main 230V supply into my garage. Yes, over my 45 year career replaced many Voltage indicators and proving units due to wear/tear and on occasion my big size 9's standing on one of them.

    Why would I wish to pay for or go thru a "Calibration" procedure? Doesn't do much that others have said above.

    In fact would likely be more economical just to purchase a new GS38 compliant voltage indicator and proving unit each year, then get them calibrated.

    GTB

  • In fact would likely be more economical just to purchase a new GS38 compliant voltage indicator and proving unit each year, then get them calibrated.

    You can have a similar conversation about calibrating torque screwdrivers, Wera say:

    For the purposes of the normative recommendations and especially in your own interest, a torque tool should be checked, calibrated and, if necessary, adjusted and/ or repaired at the latest after every 5,000 load changes or, if the number of load changes can not be determined, every 12 months.

    www.wera.de/.../EN-Torque-Tools.pdf

    Which sounds fine until you hear how much the calibration will cost, it’s better to buy a new tool with a manufacturers calibration certificate and sell the old one on an internet trading site, but they should be okay for around a hundred consumer units anyway.

Reply
  • In fact would likely be more economical just to purchase a new GS38 compliant voltage indicator and proving unit each year, then get them calibrated.

    You can have a similar conversation about calibrating torque screwdrivers, Wera say:

    For the purposes of the normative recommendations and especially in your own interest, a torque tool should be checked, calibrated and, if necessary, adjusted and/ or repaired at the latest after every 5,000 load changes or, if the number of load changes can not be determined, every 12 months.