Calibration of Approved Voltage Indicators and Proving Units.
There was an old discussion on this 7 years ago but it is locked now. In any case there was no definitive answer provided at the time. In years gone by, I would have thought that AVIs and PUs either work or they dont.
But searching online today, Martindale recommend that their AVI's and PU's do need calibrating. This has prompted me to rethink and I note that in GS38 point 30 talks about all test equipment being maintained by a competent person and one of the common errors being failing to verify correct function of illumination (eg indicator/lamp/neon).
If something were to go wrong, and it turns out the AVI and PU were not calibrated within the last 12 months, I can imagine this wording above being used to attribute blame to the person who was undertaking the proving dead.
When we prove the AVI with the PU, we are putting voltage onto the AVI and simply seeing that the lamps light up, but the PU just puts out the max voltage it is capable of, it doesnt step up or down each voltage level individually, so we dont control the level it is proving at.
What's other peoples thoughts? I am considering now that we do need to calibrate these items.
  • My proving unit steps though the voltages, also i prove it from time to time on a known good supply ( 3 phase, single phase and the continuity function),  the usual precautions of visual inspection for damage, water ingress and so on
  • You can check the output of your proving unit with your MFT, which will, of course, have been calibrated regularly.
  • What about
    https://www.testinstrumentsolutions.co.uk/voltage-testers-and-safe-isolation-kits/tis-pu1-proving-unit-for-all-voltage-testers-0-690v
  • That's an n interesting device. The manual is a bit thin, lacking any spec for how accurately it generates the various voltages,  (and I presume it also current limits and collapses the voltage at some over load level as well , which needs to be not too sensitive as some detectors need a mA or so to make them come on ) which is the sort of thing I'd like to see somewhere. However, looking at the price  it probably pays for itself the first time it finds a problem.
  • When we prove the AVI with the PU, we are putting voltage onto the AVI and simply seeing that the lamps light up, but the PU just puts out the max voltage it is capable of, it doesnt step up or down each voltage level individually, so we dont control the level it is proving at.
    That is a very valid point to discuss. It might seem like we're saying that "calibration" of the voltage detection levels is needed. Indication of voltage levels are crudely achieved by a component ladder (e.g. resistor-neon or resistor-LED), and are not designed to be that accurate overall.
    However, the voltage indicator is not intended to be an accurate display of a measured voltage ... it is, in fact, what it says on the tin "for indication purposes only" only. If you want to measure the actual voltage, use an appropriate test instrument such as calibrated MFT or GS-38 conformant, calibrated, 'electrician's multimeter', with or without an appropriate shunt resistance where necessary.
    Further 'proving dead' is not really a correct statement of what we are doing.
    Quite simply, we can't 'prove dead' because we are looking for the absence of something (electromotive force ... voltage). 'Absence of evidence is not evidence of absence' is the basic premise.
    What we are doing, is what we reasonably can do, to gather sufficient 'circumstantial evidence' there is no substantial voltage detectable.
    So, no, I don't think it's the case that a voltage indicator should be either calibrated, or relied upon for an accurate reading of voltage ... even if no lights light up, there may be some voltage there, although hopefully it's low enough not to sting us too badly !
    Don't forget also, that we are being encouraged not to rely on one detection method alone, but check the absence of EMF/voltage by other means too ... e.g. non-contact and single-pole-contact voltage detector as well ... just in case. Again, these are 'indication only' devices, i.e. can be self-checked on a known-good supply at the time of use.
    ... And then we employ further safe working practices like the use of insulated tools etc., just in case, even when we have gone through the 'making dead' procedure ... we didn't pick up someting.
  • From my understanding their support pre-sale and post sales is very good.  I am sure if you contact them they would be able to provide the information you need
    T.I.S & T.I.C
    Unit 12/14 Luddite Way Business Park
    Rawfolds Way
    Rawfolds
    Cleckheaton
    BD19 5DQ
    Test Instrument Solutions
    Tel: 01274 752407
    Fax: 01274 870175
    Email: sales@tis-tic.co.uk
    Test Instrument Calibrations
    Tel: 01274 752407
    Fax: 01274 870175
    Email: calibrations@tis-tic.co.uk
  • 'making dead' procedure
    Maybe that term could or should be changed to "NOT LIVE" as proving dead sound like statement absolute, whereas
    "NOT LIVE" or  "POTENTIALLY NOT LIVE" would be more Succinct
    I am sure the name convention would spark a very polar response.
  • Further 'proving dead' is not really a correct statement of what we are doing.
    Exactly. However, the proving unit does provide conclusive evidence that all four lamps of the approved voltage indicator are still functioning.
  • none of that is fully reliable, more of a layers of increasingly unlikely coincident  mistakes and failures.
    The big problem is often,  the indication is more of a  ' this was not live when you last looked' especially on large rambling installations with things like thermostats  time-switches and so on, its only really safe if you know it was indicating live and you know it went dead at the moment of what was hopefully isolation of the right circuits .
    There is reason that HV lines  and railways make use of shorting links while work is in progress. Yes, it is quite embarrassing if power is applied to a dead short and ADS is tested, but a lot less paperwork than a funeral.
    M
  • My point was really about terminology and Nomenclature.  Is dead or proving dead the correct term when really we are trying to prove not live with 230v AC nominal or 3 phase?  To muddy the waters further on the domestic side we could also have DC and AC in the same dwelling.  DC could be from the Solar PV or Inverter.
    eg
    The DC current from 10 solar panels depends on their wiring and wattage, typically yielding 9 to 13 Amps if wired in series, or 90 to 130 Amps if wired in parallel