Cable selection for Max fault current

For Fault at load end: The cable has to withstand the thermal stress for the through fault.

For Fault at the circuit breaker terminal side or (at the beginning of the cable): if the fault happened, it is understood that cable is already damaged, so there is no need to check the thermal stress for this case.

Refer to BS7671 clause 434.5.2, " A fault occurring at any point in a circuit shall be interrupted within a time such that the fault current does not cause the permitted limiting temperature of any conductor or cable to be exceeded"

Is the intent of this clause is that the fault do not develop in to "Fire" hazard though the cable is damaged, therefore cable thermal stress to be checked for faults at the beginning of the cable as well.

Is my understanding correct?

Parents
  • if the fault happened, it is understood that cable is already damaged, so there is no need to check the thermal stress for this case.

    That's not my understanding - all the cable should be protected where-ever the fault occurs - after all if it's a long cable, repairing/replacing a short damaged section is often much more practical than replacing the entire length up to the point of the fault.

    I think it gets confusing, as the traditional approach treated the fault-at-the-far-end as being the worst case - which was true for fuses as their energy let-through tended to increase with longer disconnection times (i.e. lower fault currents) - but with MCBs where the disconnection time is much flatter, the reverse is often the case and the worst-case for energy let-through is often close to the start of the circuit. Some text books haven't caught up I fear.

       - Andy.

Reply
  • if the fault happened, it is understood that cable is already damaged, so there is no need to check the thermal stress for this case.

    That's not my understanding - all the cable should be protected where-ever the fault occurs - after all if it's a long cable, repairing/replacing a short damaged section is often much more practical than replacing the entire length up to the point of the fault.

    I think it gets confusing, as the traditional approach treated the fault-at-the-far-end as being the worst case - which was true for fuses as their energy let-through tended to increase with longer disconnection times (i.e. lower fault currents) - but with MCBs where the disconnection time is much flatter, the reverse is often the case and the worst-case for energy let-through is often close to the start of the circuit. Some text books haven't caught up I fear.

       - Andy.