I have been looking at a domestic installation that has solar and batteries
With solar all off and isolated, and the main switch of the house CU on, but no circuits energised,
I have been looking at a domestic installation that has solar and batteries
I've checked my own house and another, and it seems within expected range, about 3.5mA
Yes very high leakage and I can't understand where it is coming from, hence why I wonder about he
solar.
DId some basic tests I haven't disconnected anything, took a Zdb and that was fine 0.12Ω
Contact voltage tests fine
IR Line-CPC fine
I've checked my own house and another, and it seems within expected range, about 3.5mA
Yes very high leakage and I can't understand where it is coming from, hence why I wonder about he
solar.
DId some basic tests I haven't disconnected anything, took a Zdb and that was fine 0.12Ω
Contact voltage tests fine
IR Line-CPC fine
T-N-C-S presumably. Fault downstream on a neighbours property causing neutral current diversion through your property? That's a total guess.
Totally isolate the PV, even the CPCs, to see if it is that causing the fault. Presumably there is an isolator on the DC side to turn that off?
Narrow down where it is coming from, as you say, anything with a CPC or a class one accessory could be the cause with a N-E fault.