I have been looking at a domestic installation that has solar and batteries
With solar all off and isolated, and the main switch of the house CU on, but no circuits energised,
I have been looking at a domestic installation that has solar and batteries
The leakage current is very high on the tails of the main board,
The main board then, not the solar/battery one? I take it you're clamping the L&N tails but leaving the earth out of it, Sounds more like a conventional fault. If it increased with load I'd suspect a N-PE fault somewhere (although it could still be that, if loads in neighbouring properties happened to be pulling the supply N up or down). The symptoms you mention sound more like rodent damage to cables to me though or damp ingress. Was you IR test done with the c.p.c.s still connected to Earth? Other possibilities might be a shared N between the sub-db and the main one - hopefully unlikely for a recent install, but maybe if there are controls/sensors involved.
- Andy.
The leakage current is very high on the tails of the main board,
The main board then, not the solar/battery one? I take it you're clamping the L&N tails but leaving the earth out of it, Sounds more like a conventional fault. If it increased with load I'd suspect a N-PE fault somewhere (although it could still be that, if loads in neighbouring properties happened to be pulling the supply N up or down). The symptoms you mention sound more like rodent damage to cables to me though or damp ingress. Was you IR test done with the c.p.c.s still connected to Earth? Other possibilities might be a shared N between the sub-db and the main one - hopefully unlikely for a recent install, but maybe if there are controls/sensors involved.
- Andy.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site