I have been looking at a domestic installation that has solar and batteries
With solar all off and isolated, and the main switch of the house CU on, but no circuits energised,
I have been looking at a domestic installation that has solar and batteries
Yes the IR test between L and E were with everything connected, (board isolated)
I have not yet disconnected any neutrals to test between N & E
This amount of leakage is new to me and I wanted to be cautious about any harmful current appearing on disconnected conductors.
There is a issue with the RCD tripping intermittently, I was just trying to see if I could narrow down the circuit with earth leakage tests by
switching on the MCBs one by one, but everything is masked by such high leakage, every circuit increases the amount of mA considerably.
With everything isolated including solar I do get 0V
I think what I need to do is isolate the main board including earthing conductor, and split the neutrals and do some proper IR tests
so basically ignoring the solar side for now. I'm comfortable with that. I have zero experience of solar, so that would need someone else.
There seems to be a gap in training for working around solar installs, and possible impacts on the installation.
Also safe isolation around solar. Plenty of courses showing you how to throw it in.
I think what I need to do is isolate the main board including earthing conductor, and split the neutrals and do some proper IR tests
Generally you leave the c.p.c.s connected to the means of earthing - otherwise you're more likely to miss damaged cables that are in contact with the general environment (e.g. damp masonry or structural steel) but not the c.p.c..
- Andy.
I think what I need to do is isolate the main board including earthing conductor, and split the neutrals and do some proper IR tests
Generally you leave the c.p.c.s connected to the means of earthing - otherwise you're more likely to miss damaged cables that are in contact with the general environment (e.g. damp masonry or structural steel) but not the c.p.c..
- Andy.
Yes I don't disconnect the cpcs