I have been looking at a domestic installation that has solar and batteries
With solar all off and isolated, and the main switch of the house CU on, but no circuits energised,
I have been looking at a domestic installation that has solar and batteries
Just as an aside, I think the OP demonstrated the merits of being equipped with an earth leakage meter. Great for fault finding but also good tool for assessing insulation resistance on periodic inspections. Much better than doing nothing and recoding +999!
Indeed - and a 'round the tails' leakage test while energised has the advantage of being a far less intrusive check.
However, there are limitations worth noting - it cannot distinguish between 'bad' leakage from slightly failing insulation, and 'good' leakage from EMC filter capacitors and so on, which a DC test can, and even the lowest easy reading of say 1mA the equivalent 250k ohms would be an insulation fail in most cases, but is of course usually capacitive. (Allow 50- 100pF per metre of cable for the core-to-core intrinsic capacitance of typical small- large cables )
Also a 3 phase all cores test, like a 3 phase RCD, may read zero or little resultant leakage when there are more or less equal larger leakages to earth on all 3 phases - or even 3 small loads connected star with the star point earthed instead of neutralled.
So long as these limitations are realised, its a jolly good test - as is the one where the same clamp meter is put on the CPC or bonding conductors to track down the stray currents, or as a risk reducing prequel to working on the earthing, by confirming that some unusually large current is not about to be interrupted and cause surprises.
Mike.
Indeed - and a 'round the tails' leakage test while energised has the advantage of being a far less intrusive check.
However, there are limitations worth noting - it cannot distinguish between 'bad' leakage from slightly failing insulation, and 'good' leakage from EMC filter capacitors and so on, which a DC test can, and even the lowest easy reading of say 1mA the equivalent 250k ohms would be an insulation fail in most cases, but is of course usually capacitive. (Allow 50- 100pF per metre of cable for the core-to-core intrinsic capacitance of typical small- large cables )
Also a 3 phase all cores test, like a 3 phase RCD, may read zero or little resultant leakage when there are more or less equal larger leakages to earth on all 3 phases - or even 3 small loads connected star with the star point earthed instead of neutralled.
So long as these limitations are realised, its a jolly good test - as is the one where the same clamp meter is put on the CPC or bonding conductors to track down the stray currents, or as a risk reducing prequel to working on the earthing, by confirming that some unusually large current is not about to be interrupted and cause surprises.
Mike.