Leakage current on installations with solar

I have been looking at a domestic installation that has solar and batteries

The solar and battery (Solar edge and Fox ESS ) are on their own sub board via henleys
The main house circuits on a split load board.
 
The leakage current is very high on the tails of the main board, round 350mA up to 700mA
With everything isolated, no leakage.

With solar all off and isolated, and the main switch of the house CU on, but no circuits energised,
I get a bump in leakage of about 15mA
When I switch on individual MCBs, I get a leap of about 100mA on some circuits and 40mA on others
with all house circuits on, but no real current draw,(nothing switch on)
I'm up past 700/ 800mA and it fluctuates up and down rapidly.
 
I thought about disconnecting the isolated solar boards main earth, but as I know little about solar
I do not want to start disconnecting anything really.
 
With isolated solar, can you still get leakage from it, which can find its way onto
the rest of the installation, and as circuits are closed, the leakage increases.
More parallel paths?

Any advice would be appreciated. Thanks
Parents
  • Just as an aside, I think the OP demonstrated the merits of being equipped with an earth leakage meter. Great for fault finding but also  good tool for assessing insulation resistance on periodic inspections. Much better than doing nothing and recoding +999!

  • Indeed - and a 'round the tails' leakage test while energised has the advantage of being a far less intrusive check.

    However, there are limitations worth noting -  it cannot distinguish between 'bad' leakage from slightly failing insulation, and 'good' leakage from EMC filter capacitors and so on, which a DC test can, and even the lowest easy reading of say 1mA the equivalent 250k ohms would be an insulation fail in most cases, but is of course usually capacitive. (Allow 50- 100pF per metre of cable for the core-to-core intrinsic capacitance of typical small- large cables )

    Also a 3 phase all cores test, like a 3 phase RCD,  may read zero or little resultant leakage when there are more or less equal larger leakages to earth on all 3 phases - or even 3 small loads connected star with the star point earthed instead of neutralled. 

    So long as these limitations are realised, its a jolly good test - as is the one where the same clamp meter is put on the CPC or bonding conductors to track down the stray currents, or as a risk reducing prequel to working on the earthing, by confirming that some unusually large current is not about to be interrupted and cause surprises. 
    Mike.

Reply
  • Indeed - and a 'round the tails' leakage test while energised has the advantage of being a far less intrusive check.

    However, there are limitations worth noting -  it cannot distinguish between 'bad' leakage from slightly failing insulation, and 'good' leakage from EMC filter capacitors and so on, which a DC test can, and even the lowest easy reading of say 1mA the equivalent 250k ohms would be an insulation fail in most cases, but is of course usually capacitive. (Allow 50- 100pF per metre of cable for the core-to-core intrinsic capacitance of typical small- large cables )

    Also a 3 phase all cores test, like a 3 phase RCD,  may read zero or little resultant leakage when there are more or less equal larger leakages to earth on all 3 phases - or even 3 small loads connected star with the star point earthed instead of neutralled. 

    So long as these limitations are realised, its a jolly good test - as is the one where the same clamp meter is put on the CPC or bonding conductors to track down the stray currents, or as a risk reducing prequel to working on the earthing, by confirming that some unusually large current is not about to be interrupted and cause surprises. 
    Mike.