Neutral in the High resistance earthed systems

For High resistance earthed, LV systems, Can the neutral be used like this? Will there be any safety issues like increase voltage in the neutral?

Parents Reply
  • The earth fault current is limited to 1A, around 25ohms

    Ah, as I know only too well,  the danger of doing sums in an open forum is that some smart!755 like me corrects you ;-) 

    Now, I reckon 230 V / 25 Ohm  is closer to 'about' 10A  To limit to 1A you'd need more like 230 ohms ;-)

    (Much like the current limit for a hard fault on a single 4ft rod TT system typically an amp or three flows in in the electrodes ,and fuses never blow, just RCDs trip.)

    I of course now am at risk of being corrected myself  if I have misunderstood the intent of the answer.

    Mike,