Machine Tool installations
I am investigating how machine tool installations should be tested and inspected. I have asked several equipment manufacturers about test certificates and they look at me blankly. In general what I have found is that the supply is tested and certified to the isolator/switchfuse feeding the machine but when the equipment is connected, there is no testing carried out on the actual kit. Does anybody have any thoughts/experience in this area. This also covers periodic inspection. I have used BS EN 60204 as a basis when I have discussed with Machine tool manufacturers.
  • Assuming (always dangerous) that you are in the UK the guiding documents would be the Machinery Directive for the machine itself and the  Provision and use of Work Equipment Regulations for its maintenance and use. Machine tools may also have their own specific standards as a subset of these two main documnets.
    Best regards
    Roger
  • Thanks for reply. I am in UK. and the equipoment is cocered by PEWUR and Machine tool directive. What I was more interested in is the first install when different cabinates and equipment is installed and interconnected but there does not appear to be any eectrical tests carried out to confirm earth loop, continuity resistance tests etc.
  • EN 60204 requires testing and verification (section 19) including continuity of the protive bonding circuit and insulation resistance. The tests shall also be carried out after any modifications. The requirement for test and inspection certainly exists. It doesn't look like it is being implemented.
    Best regards
    Roger