gkenyon:
Paul Skyrme:
My opinion here will deviate from what is stated in BS 7671, and, for some crazy reason that there has been no explanation of the product standard for RCD socket outlets (and fused connection units) have been removed from BS 7671:2018, so that could require a deviation, me, I'd not worry and fit one, including a deviation if necessary.
The requirement in BS 7671:2018 is that ALL socket outlets in domestic premises must be RCD protected.The current version of BS 7288 actually says that additional protection should already be in place within the installation. The last sentence of the first paragraph of Clause 1 of BS 7288:2016 states:
SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.
Paul Skyrme:
Yes Graham, I did look up BS 7288, some time after I responded to this thread, but it had disappeared from my forum view by then so I took at as resolved.
I feel that this is an error, of some kind, in BS 7288, which has resulted in this scenario, and this upstream requirement is the reason that the standard has been omitted from BS 7671.
This does need to be resolved by BSi/the relevant committee/JPEL64 to give the industry clarity.
At the moment devices to BS 7288 are really a device without an application, unless you really require redundant RCD protection to ensure that hopefully one goes and you don't care if the two go out in the event of a fault.
Sparkingchip:
The problem is that some LED lighting, such as patio lights that can be installed in timber decking and the like can be installed in kitchen plinths and the like, but they are supplied with a plug in LED driver or transformer.
So you need a 13-amp socket to plug the lights into the lighting circuit hidden away under the kitchen cabinets or elsewhere as you cannot cut the plug off and hard wire them.
Similar issues occur with CCTV equipment and the like, it can easily run off a lighting circuit, but needs a plug to plug the mains adapter into.
Andy B.
It should be noted as a final technical note, that SRCDs are not really an answer for fault protection (i.e. can't meet disconnection times) because they can't respond to an upstream fault. They can therefore only be used for additional protection