Nowhere do the regs say you can't have a socket on a lighting circuit
Paul Skyrme:
My opinion here will deviate from what is stated in BS 7671, and, for some crazy reason that there has been no explanation of the product standard for RCD socket outlets (and fused connection units) have been removed from BS 7671:2018, so that could require a deviation, me, I'd not worry and fit one, including a deviation if necessary.
The requirement in BS 7671:2018 is that ALL socket outlets in domestic premises must be RCD protected.
SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.
The regulations are now going for a more risk assessment based answer to most things with this not being exempt from the trail of thought. If you carried out a risk assessment that clearly defined the reasoning behind not installing a Residual Current Device would it then go towards ultimately protecting the installer from potential accusations?
Just Thoughts??