mapj1:
yes that is a "ramp test" to the older hands among us.
If you can please re-test, lying to the meter that it is an AC type, and also verify that all phase to phase voltages are similar.
how is the meter connected - how are you choosing the phases to test - your diagram may imply live no1 and earth ,
does it work if you shuffle them and use say L3 and earth ?
Is this the only RCD of its type you have tested with this meter, or has another one tested OK?
What is the NE voltage, and where is the NE bond ?
seko:
sparkiemike:
Sparkingchip:
Is it actually doing a ramp test?Don't think so, I think is the RCD tripping time because in the image the results on the instrument are in milliseconds
It is failing the test that is shown as ">1500 mA" on the display. This is a "trip-out current test" (see: Metrel 3152 manual, page 108) The "trip-out test" is described as: "The instrument increases the test current in small steps through appropriate range as follows" see page: 107.
The test stops at 1500 mA, and the test fails
Sparkingchip:
seko:
sparkiemike:
Sparkingchip:
Is it actually doing a ramp test?Don't think so, I think is the RCD tripping time because in the image the results on the instrument are in milliseconds
It is failing the test that is shown as ">1500 mA" on the display. This is a "trip-out current test" (see: Metrel 3152 manual, page 108) The "trip-out test" is described as: "The instrument increases the test current in small steps through appropriate range as follows" see page: 107.
The test stops at 1500 mA, and the test fails
I’m used to seeing ramp test results displayed to one decimal point such as in the Metrel manual example as 25.5 mA for an 30 mA RCD, but stopping to think about it small increments in the test current for an 1000 mA RCD could be 10 mA or more so the test results could be displayed in substantial incremental steps increasing the chances of the trip current being displayed as 1000 mA significantly, when it could be a bit off that.
I wonder how many increments there are between 1000 mA and 1500 mA when it fails the test, could it be going up in 100 mA steps or more?
If there’s another tester to hand it could be worth doing another RCD ramp test to try and pin down what the actual trip currents are a bit more precisely.
Andy
seko:
We have tested other RCDs of this type that have passed, but it seems to only be related to this specific installation type.
WB³:
seko:
We have tested other RCDs of this type that have passed, but it seems to only be related to this specific installation type.
Hi seko, could you clarify if you mean it is related to this specific installation, or it has happened before on this type of installation?
Is it a new installation verification or an EICR or another purpose?
seko:
WB³:
seko:
We have tested other RCDs of this type that have passed, but it seems to only be related to this specific installation type.
Hi seko, could you clarify if you mean it is related to this specific installation, or it has happened before on this type of installation?
Is it a new installation verification or an EICR or another purpose?
It has happened before "on this type of installation". It is a new installation.