As for the test that produces a 220ms for a final circuit on a TT system requiring a 0.2s disconnection time that is for once clear in 643.7.1 as it says, " The effectiveness of the automatic disconnection of the supply by RCDs shall be verified using a suitable test equipment according to BS EN 61557-6 to confirm that the relevant requirements of Chapter 41 are met, taking account of the operating characteristics of the device". So a 220ms time would not meet the requirements of Chapter 41 although it would meet the product standard. The same would apply to RCDs to the older BS 4293 standard.
Playing Devil's advocate for a moment... on a TT system is there a requirement to test a 30mA unit at 1x at all? While I can of course see the common sense in testing at 30mA, 643.8 seems only to actually require:
Also is there any value in using a lower multiple on a higher setting on the test instrument - e.g. using a 300mA x 1 as a better approximation to a 2x test for a 100mA device than a 5x 100mA test (and reduce the reliance on a low Zs in the process). Or is that instrument abuse?
On a different tangent, should we be verifying the RCD's reaction to d.c. components in the residual current too these days?
30 mA |
Conduct both 1x and 5x tests. Requires loop impedance less than 1364 Ω if you take into account full volt drop Record the 5x result. Verifies both additional protection to 643.7 and ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. Whilst the full Zs of 1667 Ω presented in Table 41.5 wouldn't provide sufficient current for a 5x test with lower voltages, earth electrode resistance should be limited to 200 Ω so no issues anticipated |
I think that I have been slightly mis-read here.
I was referring to the five tests at 1/2 Ideltan, Ideltan (x 2), and 5 Ideltan (x2). Performing them and writing them in a notebook is no bother at all.
Graham Kenyon:
Chris Pearson:
Graham Kenyon:
John,
In general, I don't really disagree with you, but ...If an RCD does not trip at 1 x Idelta n then it is defective. This softer test is a better indicator of RCD health than the 5 x test and consumer safety.
This does not unfortunately take account of a small number of cases where the RCD passes a 1x test, but then goes on to fail a 5x test, although I agree this is not simply a case of "sticky RCD".For my own peace of mind, at home, I would wish to be assured that an RCD does trip as intended. If passing at 5x means that one will also pass at 1x, then all well and good: only the one test is required. However, if not, then surely both tests are required.
Of course, there is no reason to stop doing the 5 tests, it is just that only one time needs to be recorded in the EIC/EICR (plus the all important test button).I'm still not satisfied.
RCD Residual current Rating |
---|
Tests, results and notes |
---|
10 mA |
Conduct both 1x and 5x tests Record the 5x result. Verifies both additional protection to 643.7 and ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. |
30 mA |
Conduct both 1x and 5x tests. Requires loop impedance less than 1364 Ω if you take into account full volt drop Record the 5x result. Verifies both additional protection to 643.7 and ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. Whilst the full Zs of 1667 Ω presented in Table 41.5 wouldn't provide sufficient current for a 5x test with lower voltages, earth electrode resistance should be limited to 200 Ω so no issues anticipated |
100 mA |
Conduct both 1x and 5x tests. requires loop impedance less than 409 Ω if you take into account full volt drop Record the 5x result. Verifies ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. Whilst the full Zs of 500 Ω presented in Table 41.5 wouldn't provide sufficient current for a 5x test with lower voltages, earth electrode resistance should be limited to 200 Ω so no issues anticipated If you are asserting it's unsafe to test the RCD at 5x in domestic, then do and record the 1x, but now you only have verified disconnection at 1 s and compliance with 411.3.2.4, and therefore in domestic this RCD can only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2. |
300 mA |
Not practicable (or perhaps safe) to test at 5x, so we are limited here to testing at 1x. Record the 1x result. Verifies ADS to 643.7.1 b) for 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4, but not 411.3.2.1. This leads me to assert that the 300 mA RCD may only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
500 mA |
Not practicable (or perhaps safe) to test at 5x, so we are limited here to testing at 1x. Record the 1x result Verifies ADS to 643.7.1 b) for 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4, but not 411.3.2.1. This leads me to assert that the 500 mA RCD may only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
100 mA Type S |
Conduct both 1x and 5x tests. requires loop impedance less than 409 Ω if you take into account full volt drop Record the 5x result. Verifies ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. If you are asserting it's unsafe to test the RCD at 5x in domestic, then do and record the 1x, but now you only have verified disconnection at 1 s and compliance with 411.3.2.4, and therefore in domestic this RCD can only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
300 mA Type S |
Not practicable (or perhaps safe) to test at 5x, so we are limited here to testing at 1x. Record the 1x result. Verifies ADS to 643.7.1 b) for 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4, but not 411.3.2.1. This leads me to assert that the 300 mA Type S RCD may only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
500 mA Type S |
Not practicable (or perhaps safe) to test at 5x, so we are limited here to testing at 1x. Record the 1x result. Verifies ADS to 643.7.1 b) for 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4, but not 411.3.2.1. This leads me to assert that the 500 mA Type S RCD may only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
Chris Pearson:
Graham Kenyon:
John,
In general, I don't really disagree with you, but ...If an RCD does not trip at 1 x Idelta n then it is defective. This softer test is a better indicator of RCD health than the 5 x test and consumer safety.
This does not unfortunately take account of a small number of cases where the RCD passes a 1x test, but then goes on to fail a 5x test, although I agree this is not simply a case of "sticky RCD".For my own peace of mind, at home, I would wish to be assured that an RCD does trip as intended. If passing at 5x means that one will also pass at 1x, then all well and good: only the one test is required. However, if not, then surely both tests are required.
Of course, there is no reason to stop doing the 5 tests, it is just that only one time needs to be recorded in the EIC/EICR (plus the all important test button).
Graham Kenyon:
John,
In general, I don't really disagree with you, but ...If an RCD does not trip at 1 x Idelta n then it is defective. This softer test is a better indicator of RCD health than the 5 x test and consumer safety.
This does not unfortunately take account of a small number of cases where the RCD passes a 1x test, but then goes on to fail a 5x test, although I agree this is not simply a case of "sticky RCD".