Hi everyone, I have only posted once before so thanks to anyone who replies!


I am following on from the earlier "70 volt PEN conductor not allowed to exceed post", and looking into supplying a client with an electric vehicle power supply from a three phase isolating transformer BS 7671 722.413 (1.2): " The circuit shall be supplied through a fixed isolating transformer.."


The general consensus seems to be that an external IP box with an RCD (Type B) and a tethered lead is the standard to follow, and this may be the only option with a 230 volt domestic supply, but why not use a 3 phase 400 volt step down or tapped, safety double wound isolation transformer in a standard 100 -200 ampere or above industrial units/sheds?

( Subject to load and diversity).


The answer often stated when I have asked sparks/engineers is that in-rush current are too high but a type D CB BS 60898 will 'let through' the in-rush ( the transformer manufacturer agrees), and will still give at 5 seconds- (final circuit exceeding 32 A) 0.44 ohm EL ( 10oC) , so is achievable in many situations local to Birmingham.


I was then going to run a fused cable out to an external isolated IP 65 box with a Type 2 socket to IP44 or above ( 722.55.101).


Isn't it better to engineer a solution to the upcoming electric charger deluge, rather than buying (insert well known manufacturer name here), and lots of single phase loads usually dumped onto L1?


I would be interested in any thoughts or problems you may consider....






  • SL1:




    gkenyon:




    The situation that does arise, however, is high inrush current of the rather sizeable transformers. Yes, this can be overcome, but of course costs are now increasing, and we're competing against "forget it, I'll just plug it in to a socket-outlet", which of course is far less practical, and far less safe, but doesn't have the price tag attached.



     




    Hi Mr G Kenyon,


    The original idea of my questioning the possibility of using a Double Wound Safety Transformer was to look at an alternative, ( in an industrial and offices based environment), to installing the 'box on the wall with the Type 3 sockets/tethered lead and RCD'- insert manufacturer. Your last line of your quote (above) talks about using the transformer against a socket outlet and cost ( Mode 1). Cost is big driver of bad practises, and I have witnessed at office premises a coiled extension lead plugged into a socket to charge an EV.


    My original point was that 722.413.1.2 allows for the supply of one EV from one unearthed source, using a fixed isolating transformer complying with BSEN 61558-2-4.

    So Using mode 2 ( BEAMA Guide to electrical vehicle infrastructure), with a dedicated 3 phase circuit (regular charging), a circuit breaker rated for the transformer's in-rush current type D, could be rated at 7.4 KW for industrial use using a BS 60309-02 socket, source: BEAMA Guide, subject to the vehicle protocols.

    The secondary side earth cable PE would come from the secondary side of the transformer start point.

    The Mode 2 cable providing in cable and protection device (IC-CPD) and downstream RCD protection. 


    I have asked a transformer manufacturer for costs on this and in an industrial situation, using the safety transformer, and BS 60309-02, and not duplicating an RCD in a dedicated box, could prove cheaper to purchase and install than the units currently being supplied as a standard, and spreading load across three phases would assist energy efficient electrical installations compared to single phase load balancing.

    I would appreciate any comments on this idea.


    Regards


    Simon


     




    Just a thought on this ... Regulation 722.411.4.1 provides other options for three-phase installations. However, I guess such an approach would not be precluded, provided the requisite RCDs are used as indicated in the IET Code of Practice and to meet the requirements of section 722 of BS 7671.


  • RichardCS2:



    The problem with that approach (unless I have missed something) is it only offers protection from broken CNE conductors that supply only the installation in question and carry no load currents from other installations. Given that faults most often occur at joints and that a majority of the joints are usually shared it all seems a bit dubious. Yes, in that situation there will be some benefit from the PME electrodes and potentially some from load balance, but it seems rather optimistic to think that it will always, or even usually, hold the voltage down to an acceptable level.

     



    Agreed, but this needs to be balanced against the fact that the "ME" in "PME" means "Multiple Earthing". If you follow the requirements of G12/4 for street lighting installations (and bus shelters) in this respect, the effect of other loads is lessened.


    EV charging does, in line with the point you've made, present a set of different situations - namely loads that are too large to apply similar "multiple earthing" rules, and bring anticipated touch voltages down to an acceptable level.


    Similarly, the face of modern supplies to premises has changed. We no longer have swathes of burled metal pipework supplying premises, and connected to the MET ... and in existing premises, any external metal pipework is becoming limited to the last few metres as the metal pipes int he street are being replaced with plastic. Hence, simply "progress" is changing the face of PME.


  • gkenyon:




    SL1:




    gkenyon:




    The situation that does arise, however, is high inrush current of the rather sizeable transformers. Yes, this can be overcome, but of course costs are now increasing, and we're competing against "forget it, I'll just plug it in to a socket-outlet", which of course is far less practical, and far less safe, but doesn't have the price tag attached.



     




     



    Just a thought on this ... Regulation 722.411.4.1 provides other options for three-phase installations. However, I guess such an approach would not be precluded, provided the requisite RCDs are used as indicated in the IET Code of Practice and to meet the requirements of section 722 of BS 7671.


     




    Thanks for you comments.






    However, isn't it the case that if you follow Section 722.413.1.2,  and use a Safety double insulated transformer Section 413 Electrical separation is in use.

    Therefore would the additional RCD's be required and isn't the RCD built into the manufacturers lead sufficient anyway? Surely a risk assessment could easily acknowledge that the separation system used, along with the manufacturers vehicle building-in RCD with purpose built lead and Type of socket.


    The point of the exercise was to use the transformer  protective measure rather than have the RCD so adding in the RCD on top would then defeat the idea of needing the protective separation measure, and introduce the CEN PME 70 volt rms etc problems.

     Isn't it an either/ or situation offered by Section 722?



    Regards


    Simon




     




     

  • With AC chargers, you can't get away from the RCD I'm afraid. It's not possible due to the design of the charging interface with the vehicle, which is set in standards.
  • Could one of you please draw a circuit diagram showing the electric car and battery and voltage, the DC leads; the main transformer/supply, diodes and protection fuses or circuit beakers with earthing lead arrangement so that we can all understand what is required to construct a vehicle charging station safely.  Please avoid using and initials like PME, YY or CPC  unless their are defined in words. Thank you.

  • Interestingly no one has suggested a reason why a charging RCD should be DC sensitive.



    From what I've been able to gather, it's not safe (at present) to assume that there's any galvanic isolation between the AC mains supply and the vehicle's propulsion battery & associated circuitry when on change - indeed it seems that at least one current model re-uses the charger power electronics in the power train (I'm guessing during regenerative breaking) so it's all quite tightly coupled together. It seems they don't use the traditional chassis return for the d.c. side (at least not for the propulsion system) but as usual with vehicle electrics there's only single insulation between the internal wiring and chassis. While on charge the vehicle's chassis/bodywork is likely to be connected to the supply's protective conductor. So, as one example, a single fault from say the battery circuit (at perhaps a few hundred volts d.c.) to the chassis, while on charge from a conventional TN or TT supply, would potentially mean a d.c. fault current flow from the battery, to bodywork, via the protective conductor to the EVSE and hence via the means of earthing back to the supply N point and then along the N back through the vehicle's charging circuit to the battery -ve. That d.c. fault current would be flowing through the N side of any RCDs within that loop - both on the EVSE circuit and upstream which may also protect other circuits - potentially blinding them (D-loc style) to any imbalance. Similarly faults from within the charging circuit or elsewhere in the vehicles' wiring could mean pulsed rather than smooth d.c. or at a whole variety of driving voltages.

     

    An interesting reply Andy, but the earth connection to the car is not a protective conductor in the sense of a conventional circuit, it is simply there to enable the electronics to power the car charger up. If you think about it, it doesn't provide any protection to anything, as the supply is IT, and a double fault etc. is required to get any dangerous situation.



    We might only have in mind the idea of defeating the vehicle's earth monitoring electronics, but as I see it the protective conductor between the EVSE and vehicle does a lot more than that. Both the vehicle and the EVSE potentially have exposed-conductive-parts and we can easily end up with a hazardous situation if they're not connected together in the suggested system - for example if we didn't have the protective conductor between EVSE and vehicle and the EVSE's protective conductor was connected to the separated circuit's "N" as suggested then a single L-chassis fault in the vehicle would immediately put 230V between the two parts, which are quite likely within reach of each other.


    The system as claimed isn't a IT system, but a separated one - they are slightly but significantly different (not least because exposed-conductive-parts are deliberately referenced to earth in an IT system, and if it were an IT system BS 7671 would insist on some kind of insulation monitoring).

    It would ensure that the RCD tripped if the live faulted to the car bodywork, but even so this would not be a danger to any person or livestock. If there was a neutral fault the RCD would probably trip due to current diverted via the fault, but again could in no way be considered dangerous. The "even so" means that the RCD is not the primary protection of the circuit, it is additional protection against multiple faults, single ones not being dangerous.



    But with the suggested system we've in effect built-in the first fault by connecting exposed-conductive-parts (via the EVSE's c.p.c) to a separated live conductor (let's call it "N" for the sake of argument). Our first fault (which would be a 2nd fault in a conventional separated system) now causes a large fault current to flow in the c.p.c.s and given the impedance of the protective conductors is likely to be a significant fraction of the overall fault loop impedance, create reasonable potential difference between different exposed-conductive-parts (the EVSE and vehicle for example) - so rapid disconnection (e.g. within the times of table 41.1) is then necessary to avoid danger (which is exactly what 418.3.7 tells is we need to do for 2nd faults in the general case of separated circuits). So the RCD isn't providing some additional protection, it's providing basic ADS.


    I've got in mind the video that Zoomup posted a few days ago showing the installation of EVSE (somewhere abroad) - where the "pod" clamped to a steel pole which ran through the main wiring area and was shown (quite reasonably) being earthed to the supply c.p.c. as an exposed-conductive-part. That pole was then sunk into the ground to support the EVSE - hence would be picking up an earth potential in just the same way as an extraneous-conductive-part (even if may miss being defined as such by being part of the electrical installation). If we applied the CoP's approach of supplying this though an isolating transformer but with the EVSE's c.p.c. connected to the separated circuit's "N" then what we've actually created is nothing less than a simple TN-S supply - with none of the advantages of a separated system at all (but with a lot of extra expense, both in initial costs an on-going electrical losses). We might as well just have created a TT island.


    Some of the problems could of course be mitigated if the EVSE had no exposed-conductive-parts, but that doesn't seem to be a safe assumption, especially for EVSE in public/highway areas where substantial steel enclosures seem to be the norm for mitigating against both vandalism and impact.

     

    It has been extremely difficult to design a completely satisfactory and safe car charging installation with a PME supply, and particularly with the possibility of a broken CNE. This scheme is probably as safe as is possible when cars are class 1, and I would certainly recommend that all new car designs are class 2, because that change is fairly easy and cheap, and removes the charging dangers unless damaged flexible cables are involved.



    Now there I can agree completely! (Although I anticipate some objection due to the weight of the on-board isolating transformer that would probably be needed)


       - Andy.

  • CliveS:

    Could one of you please draw a circuit diagram showing the electric car and battery and voltage, the DC leads; the main transformer/supply, diodes and protection fuses or circuit beakers with earthing lead arrangement so that we can all understand what is required to construct a vehicle charging station safely.  Please avoid using and initials like PME, YY or CPC  unless their are defined in words. Thank you.




    These are all available in the relevant standards for EV's, EV chargers, and the vehicle-charger interface.


  • AJJewsbury:




    Interestingly no one has suggested a reason why a charging RCD should be DC sensitive.



    From what I've been able to gather, it's not safe (at present) to assume that there's any galvanic isolation between the AC mains supply and the vehicle's propulsion battery & associated circuitry when on change - indeed it seems that at least one current model re-uses the charger power electronics in the power train (I'm guessing during regenerative breaking) so it's all quite tightly coupled together. It seems they don't use the traditional chassis return for the d.c. side (at least not for the propulsion system) but as usual with vehicle electrics there's only single insulation between the internal wiring and chassis. While on charge the vehicle's chassis/bodywork is likely to be connected to the supply's protective conductor. So, as one example, a single fault from say the battery circuit (at perhaps a few hundred volts d.c.) to the chassis, while on charge from a conventional TN or TT supply, would potentially mean a d.c. fault current flow from the battery, to bodywork, via the protective conductor to the EVSE and hence via the means of earthing back to the supply N point and then along the N back through the vehicle's charging circuit to the battery -ve. That d.c. fault current would be flowing through the N side of any RCDs within that loop - both on the EVSE circuit and upstream which may also protect other circuits - potentially blinding them (D-loc style) to any imbalance. Similarly faults from within the charging circuit or elsewhere in the vehicles' wiring could mean pulsed rather than smooth d.c. or at a whole variety of driving voltages.


    As I have pointed out in the Forum previously, it's as much to do with the signalling between vehicle and charger, which uses the protective conductor (and passes DC currents - pulsed and smooth).


    Quite simply, if there's a N-E fault, this DC current may be shared between N and E (definitely will be in TN-S and TN-C-S systems).


  • CliveS:

    Could one of you please draw a circuit diagram showing the electric car and battery and voltage, the DC leads; the main transformer/supply, diodes and protection fuses or circuit beakers with earthing lead arrangement so that we can all understand what is required to construct a vehicle charging station safely.  Please avoid using and initials like PME, YY or CPC  unless their are defined in words. Thank you.




    The term "PME" and "CPC" are standard terms in BS 7671. "YY" is a cable type, and appears in the On-Site Guide.


    These are all standard terms !

  • Firstly understand that the charger, which may or may not involve a transformer and diodes, is in the car, and as such is different for each model.

    Generally mains is rectified and then sliced with power transistors to provide the waveforms required to charge the batteries on that vehicle, whose number and charge characteristics are again similar but different for each model


    e.g the Zoe has a 400V battery made up of 2 paralell strings each of 96 cells in series.

    The Tesla 3 has contains 7,104 cells arranged as in 16 parallel banks each containing further parallel strings  of about 350V each.


    There is no 50Hz isolation transformer as such,  the switching frequency is supersonic. These block diagrams of what is in a typical car may help


    a55e9f81d5194c4a72c382eec1f2cd56-huge-ev-hev1.jpg
    a29a5070ba2294183ef41d0ef719d78f-huge-ev-hev2.jpg




    All the current generation of charging  points do is  to close a contactor to provide a connection to the mains when certain interlock conditions are met.

    If you understand circuit diagrams, this here is a delightfully simple but fully standard compliant example of the sort of thing you may have in the wall box, and is in the public domain.

    Better still there is a full description of how it meets that standard also on the web here