(a 13A fused load, a 13A switch, a 16A cb)
AJJewsbury:
(a 13A fused load, a 13A switch, a 16A cb)
That's interesting - I've never come across a 13A grid switch - usually they're 5/6A, or 20A. 13A markings on BS 1363 accessories yes, but not grid. I wonder if the switch element had been re-purposed from a FCU (some brands seem to make them up from grid-like components).
- Andy.
Farmboy:
Had an interesting chat with a tech dept this afternoon after coming across some grid switches in a domestic kitchen.
Four grid switches (sharing a common backbox) are each fed via their own 16A cb's, and each feeds 1G sockets (for a cooker hood, fridge freezer, etc). Ignoring the cable sizes (the focus being on the grid switches), given the 13A plug fuses limits the loads in each cct, would you have the current rating of the grid switches equal to or higher than the 16A cb's (e.g. 20A), or lower (but equal to or higher than the socket rating e.g. 13A/14A)?
F
Alasdair Anderson:
Zoomup:
Any switch controlling a 13 Amp socket must be able to carry at least 13 Amps. That is what the 13 Amp socket can supply. A grid switch rated at 16 or 20 Amps could be used.
Z.If the socket has a BS 1363 plug fitted with a BS 1362 fuse rated 13A then it could be supplying 20 for a significant period (>3hours). Take a look at the fuse characteristics
.
Presumably the single 13 Amp sockets are behind the appliances like the fridge freezer, or at high level above the extractor hood, so are very unlikely to be used for additional appliances. That is why there are conveniently positioned grid control switches. Therefore this is a non-issue. A 10 Amp grid switch will not catch fire or blow up if carrying 11 Amps in most cases. A 20 Amp grid switch will be fine for other appliances like washing machines or tumble driers etc. Overloading is very unlikely if the single 13 Amp sockets are inaccessible. Stop worrying needlessly.
AJJewsbury:
Presumably the single 13 Amp sockets are behind the appliances like the fridge freezer, or at high level above the extractor hood, so are very unlikely to be used for additional appliances. That is why there are conveniently positioned grid control switches. Therefore this is a non-issue. A 10 Amp grid switch will not catch fire or blow up if carrying 11 Amps in most cases. A 20 Amp grid switch will be fine for other appliances like washing machines or tumble driers etc. Overloading is very unlikely if the single 13 Amp sockets are inaccessible. Stop worrying needlessly.
Ah, but you're only considering overload - what about fault currents?
- Andy.
What about fault currents? 559.5.1.204 allows a lighting circuit to be protected by an over current protective device up to 16 Amps, but we generally use 6 Amp rated light switches. There is normally no problem with that.
Neither the light switch nor the grid switch has to survive after closing onto a fault, and probably won't
wallywombat:
Bear in mind that a single socket could have a 2-way unfused 'cube' adaptor plugged into it, effectively turning it into a double socket, where 20A may flow (but never 26A, because that never happens, because Reasons),