gkenyon:
This leads to the question "Is it OK for a tumble dryer and a washing machine to be simultaneously plugged into a double socket-outlet?"
Answers on a postcard to ...
gkenyon:
wallywombat:
Bear in mind that a single socket could have a 2-way unfused 'cube' adaptor plugged into it, effectively turning it into a double socket, where 20A may flow (but never 26A, because that never happens, because Reasons),Being a little devilish ...
Double socket-outlets to BS 1363-2 are now (to the current standards) rated at 13 A. Single socket-outlets are also rated 13 A.
This leads to the question "Is it OK for a tumble dryer and a washing machine to be simultaneously plugged into a double socket-outlet?"
Answers on a postcard to ...
AJJewsbury:
Presumably the single 13 Amp sockets are behind the appliances like the fridge freezer, or at high level above the extractor hood, so are very unlikely to be used for additional appliances. That is why there are conveniently positioned grid control switches. Therefore this is a non-issue. A 10 Amp grid switch will not catch fire or blow up if carrying 11 Amps in most cases. A 20 Amp grid switch will be fine for other appliances like washing machines or tumble driers etc. Overloading is very unlikely if the single 13 Amp sockets are inaccessible. Stop worrying needlessly.
Ah, but you're only considering overload - what about fault currents?
- Andy.
Zoomup:
No it can't supply 20 Amps for hours. These are apparently single 13 Amp sockets for individual dedicated appliances like a cooker extractor hood and fridge freezer etc., so the loads are fixed. No overloading can occur.
Z.
Chris Pearson:
gkenyon:
This leads to the question "Is it OK for a tumble dryer and a washing machine to be simultaneously plugged into a double socket-outlet?"
Answers on a postcard to ...Ours have been for the past 20-odd years. ?
Of course, it depends upon the machines. Ours total 5.15 kW = 22 A, which exceeds a double socket's rating of 20 A until diversity comes into play.
It must be that every BS1363 socket can safely supply 13 A indefinitely because that is what users are entitled to expect of them.
Er, well the ones marked "EV" are supposed to be able to - which does rather beg the question of the others...
It is not expressly stated, but if a twin socket-outlet may safely supply 14 A + 6 A for at least 4 hours with a stable temperature, it may be inferred that it is safe to do so.