Chris Pearson:
AJJewsbury:
Am I reading this differently from everyone else? If a 'multiple socket outlet' is a combination of two or more socket outlets and the rated current of all socket-outlets shall be 13A, surely this means a multiple socket outlet with two socket outlets must be rated at 13A + 13A, or 26A for the unit. Or is this wrong?
... e.g. you could take the full 13A from either the left hand outlet, or the right hand one, but not necessarily both together ...
It would be absurd if one could take the full 13 A from one side of a twin socket and nothing from the other - there would be no point in having a twin socket.
gkenyon:
No-one would make the same statement about a 4-way (or 6-way or 10-way) "extension" with a 13 A plug, now, would they?
That's completely different - the total output is limited by the fuse in the plug, and possibly another one in the sockets.
MK make a triple 13 A fixed socket, but they are collectively fused in the same way by a BS 1362 fuse. Their literature specifies a rating of 13 A for singles and doubles, but 13 A total for triples. It does not say 13 A total for doubles.
Chris Pearson:
gkenyon:
No-one would make the same statement about a 4-way (or 6-way or 10-way) "extension" with a 13 A plug, now, would they?That's completely different - the total output is limited by the fuse in the plug, and possibly another one in the sockets.
MK make a triple 13 A fixed socket, but they are collectively fused in the same way by a BS 1362 fuse. Their literature specifies a rating of 13 A for singles and doubles, but 13 A total for triples. It does not say 13 A total for doubles.
perspicacious:
Historically when spurring off a ring final circuit, were you only allowed one double or if in different rooms, a single in each of those?
Regards
BOD
-2400-:
To add to the chance of confusion, the MK technical data for Logic Plus range states:
Current rating
13A
(3 Gang Switchsocket 13A total)
which without any further information, it would be reasonable to interpret as though the 2 gang was 2 x 13A, otherwise they might have written
(2 Gang and 3 Gang are 13A total)