Chris Pearson:
BS1363-2:2016+A1:2018
<snip>
Section 6: classification and rating
6.1 The rated current of all socket-outlets shall be 13 A
<snip>
Section 16 specifies 14 A + 6 A for temperature testing.
It must be that every BS1363 socket can safely supply 13 A indefinitely because that is what users are entitled to expect of them. Nowhere does it say that the total of a multiple socket-outlet is limited to 13 A. It is not expressly stated, but if a twin socket-outlet may safely supply 14 A + 6 A for at least 4 hours with a stable temperature, it may be inferred that it is safe to do so.
Chris Pearson:
BS1363-2:2016+A1:2018
Section 3: definitions
"socket-outlet" accessory having a set of three socket-contacts designed to engage with the pins of a corresponding plug ...
"multiple socket outlet" combination of two or more socket outlets
Section 6: classification and rating
6.1 The rated current of all socket-outlets shall be 13 A
Section 16 specifies 14 A + 6 A for temperature testing.
It must be that every BS1363 socket can safely supply 13 A indefinitely because that is what users are entitled to expect of them. Nowhere does it say that the total of a multiple socket-outlet is limited to 13 A. It is not expressly stated, but if a twin socket-outlet may safely supply 14 A + 6 A for at least 4 hours with a stable temperature, it may be inferred that it is safe to do so.
Am I reading this differently from everyone else? If a 'multiple socket outlet' is a combination of two or more socket outlets and the rated current of all socket-outlets shall be 13A, surely this means a multiple socket outlet with two socket outlets must be rated at 13A + 13A, or 26A for the unit. Or is this wrong?
AJJewsbury:
Am I reading this differently from everyone else? If a 'multiple socket outlet' is a combination of two or more socket outlets and the rated current of all socket-outlets shall be 13A, surely this means a multiple socket outlet with two socket outlets must be rated at 13A + 13A, or 26A for the unit. Or is this wrong?
... e.g. you could take the full 13A from either the left hand outlet, or the right hand one, but not necessarily both together ...
gkenyon:
I've seen similar situations where the plug and socket-outlet are not overloaded, say appliances running at about 2 kW, but bad connections in the plug (loose terminal screw, or, with moulded plug, similar cases such as broken strands on crimps or brazing)