gkenyon:
So "it would be reasonable to interpret" is in my opinion an assumption at best.
-2400-:
To add to the chance of confusion, the MK technical data for Logic Plus range states:
Current rating
13A
(3 Gang Switchsocket 13A total)
which without any further information, it would be reasonable to interpret as though the 2 gang was 2 x 13A, otherwise they might have written
(2 Gang and 3 Gang are 13A total)
perspicacious:
Historically such as in the 15th edition of 1987 a non fused spur could only supply one single or one twin (double) socket outlet from a ring.
My history goes back further as A.40 in the 14th (1966 through to 1976) states: "Not more than two socket-outlets, or one twin socket-outlet, or one stationary appliance, shall be fed from each non-fused spur."
Whilst the wording of the 13th 114 (B) (ii) is similar, it doesn't define socket-outlets as being single or twin though
Regards
BOD
-2400-:
gkenyon:
So "it would be reasonable to interpret" is in my opinion an assumption at best.
Which is the point I was making.. ie WITHOUT FURTHER INFORMATION it is quite likely that the data sheet could be interpreted that way. Hence adding to the confusion, as I said.
I do hope you didn't assume I was disagreeing with anything you said ?
Chris Pearson:
-2400-:
To add to the chance of confusion, the MK technical data for Logic Plus range states:
Current rating
13A
(3 Gang Switchsocket 13A total)
which without any further information, it would be reasonable to interpret as though the 2 gang was 2 x 13A, otherwise they might have written
(2 Gang and 3 Gang are 13A total)Glad not to be alone on this one, but equally well they have not specified 2 x 13 A.
I maintain that a twin socket is rated at 14 A + 6 A. That is not necessarily the same as, for example, 10 A + 10 A. It may be more or less onerous.
gkenyon:Chris Pearson:
Glad not to be alone on this one, but equally well they have not specified 2 x 13 A.
I maintain that a twin socket is rated at 14 A + 6 A. That is not necessarily the same as, for example, 10 A + 10 A. It may be more or less onerous.The standard does not say that. It says:
- The double socket-outlet is stress tested with 14 A + 6 A loads connected.
- The manufacturer marks the rating on the accessory
In the case of a double socket-outlet, the rating is clearly marked (on the rear) with, usually, 13 A these days.
Chris Pearson:
So what do we mean by the word, "rating" which is in the subject heading?
If MK states that it's twin sockets may supply a combined current of 19.5 A continuously, why are they not rated at 19.5 A? If such ratings were applied, purchasers might choose to buy the sockets with a higher rating so competition might drive up the quality.
If a multiple socket-outlet may safely supply only 13 A, why are they not required to have a 13 A BS 1362 fuse in them?
The 1984 version of the standard is the same as the current one as regards labelling. Unfortunately, the original 1947 standard is not downloadable from the BS site.
I am tempted to put a clamp meter on the circuit when both washing machine and tumble drier are running.
I can tell you what you will see for domestic machines, which is as follows:
On high heat, the tumble dryer will use about 1-2 A when only the motor is running, and 11-12 A when both parts of the element is switched on. Depending on the weather (temperature and humidity), and how damp the clothes are, the highest current is drawn between 40 and 80 % of the time.
The washing machine (washer only - not washer-dryer) is roughly similar - slightly more motor current on spin - but only draws its full power of approximately 11 A when heating. On a boil wash in winter, time to get to temperature can be a considerable time. However, on most cycles in use, I'd guess the heater on a modern machine is on for about 10 minutes at most.
A dishwasher heater is on for longer - especially where the machine has a drying cycle at the end also.
So, in a domestic situation, you will get about 24 A for periods of 10-30 minutes at a shot, probably meaning many double socket-outlets would deteriorate in a couple of years at most, dependent on usage - greater risks in winter.
Commercial / industrial usage is a very different kettle of fish.