Question about BS EN 12101-6:2005, art. 11.6.3
The article 11.6.3 in BS EN 12101-6:2005 states the requirements for electrical cables used in pressure differential systems:
    a) fire-resisting cables meeting the temperature and time criteria in accordance with Table 7 or
    b) enclosed with fire-resisting construction, or installed external to the building where the cables cannot be endangered by fire, and
    c) cables protected from fire shall comply with the classification temperature/time of the component that they serve.
I'm reading again and again and I'm still not sure if the conditions should be met as follows:
    1. ( a or b ) and c
    2. a or ( b and c )
Please help.
  • I read it as 2. (a), OR (b) and (c).
    So, (a) on its own
    OR (b) and (c) together.
    I suspect the correct answer is:
    1. ( a or b ) and c
    OMS
  • I have two contradictory answers.
    Could you expose your arguments, please?
  • A or B and C.
    Whether you chose fire resistant cables or protect non- fire resistant cables by other means, their integrity has to be maintained to the time/temperature rating of the equipment they serve.
    burn
  • From the logic - let us assume the cable has to reach some piece of equipment that operates under conditions T1 P1,
    and the cable route  to get there must pass through a region of environment  P2 T2, which is more stressful than T1 P1
    If the cable is not otherwise protected then clearly it must pass T2 P2 and will also pass the lower stress P1 T1.
    If sheltered from the rigours of the P2 T2 environment by suiatable containment, it need only pass the worst condition to which it is exposed, whcih may be now P1 T1, or still the condition inside the enclosure, depending which is worst.
    Both answers above are the same, so  long as T2>T1 and P2 > P1.
    It might have been better if they said ' adequate for the conditions through which it passes and the termination conditions, whichever is more stressful.'
    It is then clear that when shielded, the condition through which it passes may no longer be the dominant, and if so you must consider the termination conditions as setting the harder limit.
    Of course, the temperature limit may be highest in one region but some other parameter, I could imagine humidity, corrosive gasses, sand storms, whatever, may be worse in another, the cable must of course be selected and protected to  survive both...
  • a or (b and sometimes c)
    because the first option is to have fire-resistant cables, which comply with the requirements of table 7 - i.e. they can withstand temperatures of 300°C to 600°C
    the second option is to protect the cables (b1) or site them where they will not be exposed to fire (b2)
    if the cables are protected (b1) they must be at least as durable as the component which they serve - e.g. a fan; but if the cables cannot be exposed to fire, they don't in fact need to be fire-rated at all.
  • It seems that everyone is coming up with a different interpretation. The only solution seems to be to ask the people who wrote it. The BSI committee involved is FSH/25 so an email to them may provide an answer (if you can find out who to contact) and if they are unable to answer they can pass it to the parent international committee which seems to be CEN TC191/SC1.