Andy, you're quite right, and this is what's described in section 5.3.4 of the IET Code of Practice for EV Charging Equipment Installation (3rd Edition, but it's been in there since the 1st Edition with no-one worrying about it). Provided that ALL of the following are met, it should be OK for Electrical Separation:
- the protective conductor on the secondary is not connected to any conductor (including protective conductor) of the primary
- Isolating transformer meets requirements for electrical separation
- There is an RCD (30 mA for EV supply equipment) immediately after the secondary.
- Only one vehicle is supplied by each transformer (one transformer per charge point).
(Side note: for those that are still a little queasy about the situation, unearthed systems with protective conductors are discussed in BS 7430 ... as Andy says it's not really covered in sufficient detail in BS 7671 at the moment ... but I really don't think this particular situation needs to go down that rabbit hole as it's one separated system feeding one vehicle as per Section 722.)
I essentially am part of the install only as the client provides their own charge points which are all pre-built and shipped over, but I'm sure if we can come to an agreement or a redesign then this could change. We install mainly 7kW and 22kW charge points.
500kW of EVC's Is one hell of a lot. I know Tesla have unveiled a 250kW charge point which requires a 1MW transformer to power 4 of them but we simply don't have the infrastructure to cope with that at the moment. I was asked to look at an install elsewhere as someone wanted to know how many 50kW rapid chargers would fit in the car park - long story short, they didn't go with it as it required a new HV supply to a brand new substation for a few charge points which would have been too powerful for the nature of the car park. (you wouldn't really have a 50kW in a "Park & Ride" as chances are you're going to be a good few hours!), if you need any help with this then I'll be happy to lend some assistance where I can.
411.3.1.1 Protective earthing
Exposed-conductive-parts shall be connected to a protective conductor under the specific conditions for each type of system earthing as specified in Regulations 411.4 to 411.6.
Simultaneously accessible exposed-conductive-parts shall be connected to the same earthing system individually, in groups or collectively.
AJJewsbury:
411.3.1.1 Protective earthing
Exposed-conductive-parts shall be connected to a protective conductor under the specific conditions for each type of system earthing as specified in Regulations 411.4 to 411.6.
Simultaneously accessible exposed-conductive-parts shall be connected to the same earthing system individually, in groups or collectively.
Curiously, the same demand doesn't seem to be made of extraneous-conductive-parts (even though they are likely connected to the same MET as an exposed-conductive-part).
Steel lighting columns, I would suggest, are generally extraneous-conductive-parts rather than exposed-conductive-parts (the innards generally being sheathed cables and enclosed terminals/devices). Even contact with the class I lighting head on the top and/or a deliberate bond to the lamppost's MET doesn't make it an exposed-conductive-parts (even though it would obviously attain the same potential).
So it might be that the only actual exposed-conductive-parts with reach are the charge point (if metallic) and the car itself (when present) - which would make satisfying 411.3.1.1 easy.
What if we had a TT system for the EVSE and if we felt the need bonded the TT MET to any extraneous-conductive-parts in the vicinity (e.g. lighting columns). Very much like a TT'd house sharing a metallic water main with the PME'd house next door. Clearly nonsense from the point of view of avoiding nasty touch voltages under broken CNE conditions, but doesn't actually seem to be against either the general rules of BS 7671 or section 722 in particular (only the 'means of earthing' is prohibited from using PME - not parallel paths via extraneous-conductive-part).
- Andy.
If the extraneous-conductive-part is bonded to one installation already, and you then bond it again to another installation, the second protective conductor [main protective bonding conductor] surely becomes common to both installations.
But the idea that they are not bonded is something of a mistake, reliable isolation cannot be acheived, adjacent buildings share gas and water pipes accross multiple methods of earthing (TT and PME is commonly mixed on farms, where the house is PME, and the farm proper is very much TT. Both have water. Mixed TNC-s and TNs on the same substation is common in built up areas with mixed ages of property), not to mention water and gas pipes also interlinking the CPCs of multiple substations.
perhaps we need to permit fuses and breakers in the CPC after all ?
mapj1:
If the extraneous-conductive-part is bonded to one installation already, and you then bond it again to another installation, the second protective conductor [main protective bonding conductor] surely becomes common to both installations.
But the idea that they are not bonded is something of a mistake, reliable isolation cannot be acheived, adjacent buildings share gas and water pipes accross multiple methods of earthing (TT and PME is commonly mixed on farms, where the house is PME, and the farm proper is very much TT. Both have water. Mixed TNC-s and TNs on the same substation is common in built up areas with mixed ages of property), not to mention water and gas pipes also interlinking the CPCs of multiple substations.
perhaps we need to permit fuses and breakers in the CPC after all ?